I have a portable generator that I would like to use to run a well pump. The well is not currently hooked to the house. Now my question......The generator has a 4 prong plug for 220. The well has only three wires going to it. two hots and a ground. Is it possible to hook the three wires to a four prong plug and if so, what do I do with the fourth prong. Leave it empty? I am guessing the 4 prongs are (2) hots, (1) neutral, and (1) ground.

TIA
 
To avoid these ads, REGISTER NOW!

Ezzie

Well-known member
Joined
Oct 15, 2007
Messages
371
Location
Lake Chapala, Jalisco
You didn't specify what the voltage of your pump is nor the capacity of your generator. If it has a 4 prong plug it is probably at least a 5000W unit with a 220V 20A twist lock plug. Make sure you know what voltage your pump is before you do the following.

Assuming it is a 220V pump, you do not need the neutral in the 4 prong plug. Wire the two hots (usually black & red or the X & Y designations in the plug) and the green ground (designation G with a green screw terminal in the plug). Ensure your generator is switched to the 220V position and you should be good to go.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
the generator needs to be really oversized compared to the draw of the motor to be able to start it.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,068
Location
Coronado, CA
Everything needs to be connected to a common ground in the event that there should be an insulation failure (short circuit).

Assuming ( a dangerous practice ) The center wire on the 3 Prong Plug is the ground, it would be connected on the 4 Prong Plug to the blade with the bump going to the side.

The generator set needs to be connected to ground, see your instruction book. I keep a ground rod in my "what if" collection in case there is no suitable ground when away from my shop.
 
OP
K

Kevin54

MEMBER EMERITUS
Joined
Jan 12, 2005
Messages
29,341
Location
Urbana, Ohio
You didn't specify what the voltage of your pump is nor the capacity of your generator. If it has a 4 prong plug it is probably at least a 5000W unit with a 220V 20A twist lock plug. Make sure you know what voltage your pump is before you do the following.

Assuming it is a 220V pump, you do not need the neutral in the 4 prong plug. Wire the two hots (usually black & red or the X & Y designations in the plug) and the green ground (designation G with a green screw terminal in the plug). Ensure your generator is switched to the 220V position and you should be good to go.

Sorry about that. Too many things on the old mind today. The well pump is 220, the generator is 5700 watts and the generator has a 30 amp 4 prong twist plug. No switch between the 110 and 220 on the generator. There are (2) 110 plugs and (1) 220 plug
 
To avoid these ads, REGISTER NOW!
OP
K

Kevin54

MEMBER EMERITUS
Joined
Jan 12, 2005
Messages
29,341
Location
Urbana, Ohio
It's a 1/2 horse, 12 gpm, 230v pump. The only paperwork that I have is a sticker on the breaker panel that states "T12-50 Aermotor" which I believe is a Franklin (?) pump
 

ArthurPE

Banned
Joined
Jun 14, 2009
Messages
423
1/2 HP should be <1 KW, even with a poor power factor, closer to 500 W

a 5700 W (~7.5 HP) genset has plenty of oomph to start it...as long as it's not loaded up with other stuff...
 
OP
K

Kevin54

MEMBER EMERITUS
Joined
Jan 12, 2005
Messages
29,341
Location
Urbana, Ohio
Got it done. No load at all on the generator. But wow!!!!!!! The plugs are not the cheapest things. $30 for a plug is kind of steep I thought, but if you don't have one you have to shell it out. I checked at Lowes and our local Ace Hardware and neither had them, so I had to go to the electrical supply house. At least now if the power goes out I can have water. LOL!!! Really my main concern was that the well has not been used in a couple of years and I was worried that the pump may have been frozen up. Hopefully this week I can get power from the main out to it and hooked back up permament. Thanks all for your help. :thumbup:
 