So the air conditioner was on and running but no air was coming out of the vents. Even with the fan on mode, no air blowing out.
Furnace is around 20 years old.
Upon closer inspection the furnace blower motor wasn't spinning.
I could spin the blower motor by hand and it would keep going. But it won't start by itself.
The capacitor had a small deformation in the top of the cap.
For $10 I ordered a new capacitor and it fixed the problem.
Question is, how often are these prone to going out?
Furnace is around 20 years old.
Upon closer inspection the furnace blower motor wasn't spinning.
I could spin the blower motor by hand and it would keep going. But it won't start by itself.
The capacitor had a small deformation in the top of the cap.
For $10 I ordered a new capacitor and it fixed the problem.
Question is, how often are these prone to going out?