First post! I've read through lots of posts on Garage Journal and others. Very good information and I want to run my electric plan by those with experience here.
Background
I have two detached buildings on my property: a 3+ car garage and a new 30x40 pole barn. I'll refer to these as the "garage" and the "barn".
My proposal & questions:
I am planning to run power from the panel in my existing detached garage to the new barn. Running power direct from the house would be farther, and in addition there are several obstacles in the way (septic, gas line, and tree roots). It's 324ft from my existing garage panel to where the new barn panel will be. About 275ft of this will be buried in conduit and the other 50ft running in conduit inside the garage.
Based on my research I am thinking of running either 6ga stranded copper or 2/2/2/4 aluminum USE-2 Mobile Home Feeder in 1-1/2 conduit. According to the Southwire voltage drop calculator, both of these options would only allow 20A at my barn.
My questions are:
Background
I have two detached buildings on my property: a 3+ car garage and a new 30x40 pole barn. I'll refer to these as the "garage" and the "barn".
- House - 200A service
- Garage - currently fed by approximately 100ft of 6ga copper stranded wire (4-wires in conduit) protected by a 60A breaker in the house. This is my primary shop and work area. I have a small welder and air compressor that I use occasionally, but no other large loads. Mostly I am doing woodworking and light automotive projects. I have never tripped the 60A breaker.
- Barn - this is a new 30x40 pole building with no electric service yet. This building will mainly be cold storage, however I would like electricity for basic lighting, battery maintainers, security cameras (light loads). I want to plan for the future but without going overboard - especially with current wire prices.
My proposal & questions:
I am planning to run power from the panel in my existing detached garage to the new barn. Running power direct from the house would be farther, and in addition there are several obstacles in the way (septic, gas line, and tree roots). It's 324ft from my existing garage panel to where the new barn panel will be. About 275ft of this will be buried in conduit and the other 50ft running in conduit inside the garage.
Based on my research I am thinking of running either 6ga stranded copper or 2/2/2/4 aluminum USE-2 Mobile Home Feeder in 1-1/2 conduit. According to the Southwire voltage drop calculator, both of these options would only allow 20A at my barn.
My questions are:
- Can I really only get 20A out of 6ga copper or 2/2/2/4 aluminum at this distance? The guys building my building are currently using 300ft of 16ga cheap extension cords to run their compressor and chargers. I'm not saying that's right, but it seems crazy that I would need such larger wires for the panel.
- I've done a lot of wiring with copper, but never aluminum. Any reason not to go with aluminum in this application?
- Any issue with running PVC conduit inside the garage and through the attic?