Asking for a friend..........he wants to mount a 45k Hot Dawg on a shelf, mounted to a wall in his garage

Vent will be CAT III, ran horizontal

Any issues with clearance issues to "combustibles" when setting the heater down onto a shelf made from wood (2x4s and plywood)?

What about a rubber mat under the heater to help with vibrations?
 
To avoid these ads, REGISTER NOW!

ezridr60

Well-known member
Joined
Dec 16, 2011
Messages
202
Location
Iron River, MI
I’ve got a 2 Sterling Garage Guy 75,000BTU heaters, similar to Modine Hot Dawg. This is from the install manual.

“CLEARANCES: Each Gas Unit Heater shall be located with respect to building construction and other equipment so as to permit access to the Unit Heater. Clearance between vertical walls and the vertical sides of the Unit Heater shall be no less than 1 inch (25.4mm). However, to ensure access to the control box and fan, a minimum of 18 inches (457mm) is required for the fan, and control box side. A minimum clearance of 1 inch (25.4mm) must be maintained between the top of the Unit Heater and the ceiling. The bottom of the Unit Heater must be no less than 1 inch (25.4mm) from any combustible. The distance between the flue collector and any combustible must be no less than 1 inch (25.4mm). Also see AIR FOR COMBUSTION and VENTING sections.
NOTICE: Increasing the clearance distances may be necessary if there is a possibility of distortion or discoloration of adjacent materials.”

I would assume the Modine unit is similar, but you should be able to view a Modine manual online to be sure
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
What I read is nothing can be under the heater. For a horizontal exhaust you need 5’ of pipe so even if you have a bend or two you will be about 3 feet from one wall. The other sides and top of the heatercsn be closer.
 
Last edited:
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,530
Location
Minneapolis
This is from the Hot Dawg owners and installation manual:


Shelf mounted units: The unit heater can also be installed on a shelf. The mounting brackets will need to be attached to the heater the same manner as explained in note #4, however, to mount on a shelf the brackets must go on the bottom of the heater. The brackets must be affixed to the shelf using similar screws (1/4" screw with 1/2" washer) as overhead joist or truss mounting. Be sure all clearance to combustible requirements are met.

attachment.php




You can download the whole manual here: http://www.modinehvac.com/web/produ...-heaters-hotdawg/hot-dawg-power-vented-hd.htm
[FONT=Arial,Arial][FONT=Arial,Arial][FONT=Arial,Arial]

[/FONT]
[/FONT]
[/FONT][FONT=Arial,Arial][FONT=Arial,Arial]

[/FONT]
[/FONT][FONT=Arial,Arial]
[/FONT]
 

Attachments

  • hot dawg clearances.jpg
    hot dawg clearances.jpg
    30.5 KB · Views: 153
To avoid these ads, REGISTER NOW!
Top Bottom