How I'm I doing? pic.

To avoid these ads, REGISTER NOW!
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
I was thinking that I could save on wire if I put it that high.:spit: Just kidding, I just haven't driven it in yet.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I'll just rattle off a few things in case you missed them or maybe you just haven't got to them yet:

1. Roof jack goes under the shingles.
2. Around here we install the insulator knob on the mast for power co. to attach too.
3. You need to mark your neutrals white.
4. Don't forget to tighten that locknut on the offset ******.
5. Don't forget to run the green bond screw into the can.
6. PVC needs a plastic bushing.
7. If there is more than 3' between the top of the meter can and soffit, you need a strap.
8. The PVC also needs a strap within 3' of the can.
9. Some jurisdictions also require sch. 80 to be used where pvc is exiting the ground. Some also require expansion fittings too.

Maybe this will help you.:)
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
I'll just rattle off a few things in case you missed them or maybe you just haven't got to them yet:

1. Roof jack goes under the shingles.
2. Around here we install the insulator knob on the mast for power co. to attach too.
3. You need to mark your neutrals white.
4. Don't forget to tighten that locknut on the offset ******.
5. Don't forget to run the green bond screw into the can.
6. PVC needs a plastic bushing.
7. If there is more than 3' between the top of the meter can and soffit, you need a strap.
8. The PVC also needs a strap within 3' of the can.
9. Some jurisdictions also require sch. 80 to be used where pvc is exiting the ground. Some also require expansion fittings too.

I just got though putting the roof jack under the shingles. and the insulator knob.
Good eye ,some how when I got home from the big box store one of the plastic bushing was missing.
I have the straps I will intall them tomorrow.
It's sch. 80 pvc. I didn't know about the expansion. Is it a big deal not to have one?
I also have to get a ground strip.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
Is it just the picture, or is the (top of the) cap sitting on top of the shingles.:headscrat If so, why:confused:


Your right it's sitting on top of the shingles. I may of sanped the pics. a little to soon, but I was happy just getting the boxes and cables installed. I had to show someone. :lol_hitti It's under the shingles now.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
is that in pipe all the way? Or is the cable buried in the ground? What size is that ground?

you need to tape your neutrals white.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
is that in pipe all the way? Or is the cable buried in the ground? What size is that ground?

you need to tape your neutrals white.

Yes it's in pipe all the way. I just got back from lowes with some white tape. The ground wire is #8, But for the grounding rods I have #4 I'm putting two rods six feet apart at the service, and adding another ground rod at the house :thumbup:
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
oh, do you have the other end of this put together yet? post some pics of it if you do.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
dont you need #6 EGC for 200a?

I still can't find anyone around here that thinks I need the ground wire, but I ran it anyways. I had the #8 already so that's what I went with. The outher end still has the live meter. I have a samll Junction box that I will put where the old meter is. I plan to use something a supply store had to connect the ends. I don't remember what they called it but it was rubberized and had two ports the middle for the cable and allen head screws at the ends, after you thighen the ends it has caps to close it up. It's a bit pricey $20.00ea. but I think it's better then the rubber tape.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you need the ground wire, 100%, no doubt about it. Why do these people think you dont need it?
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I didn't know about the expansion. Is it a big deal not to have one?

Depends on if you have a lot of ground movement or not.

I plan to use something a supply store had to connect the ends. I don't remember what they called it but it was rubberized and had two ports the middle for the cable and allen head screws at the ends, after you thighen the ends it has caps to close it up. It's a bit pricey $20.00ea. but I think it's better then the rubber tape.

They're known as insulated taps. Burndy and Polaris are a couple brands.

I still can't find anyone around here that thinks I need the ground wire, but I ran it anyways.

Because everyone around there seems to be clueless about code compliant electrical work.

you need the ground wire, 100%, no doubt about it. Why do these people think you dont need it?

See response above.

dont you need #6 EGC for 200a?

Yes, #6 Cu.

4/0 alum wire needs a #4 copper or #2 alum grounding conducter.

You will also need a ground wire to the water pipe and gas pipe, if any, again#4 copper or #2 alum.

First sentence is wrong, second sentence is right. You're looking at the wrong table, try Table 250.122. There are seperate tables for equipment grounding conductors and grounding electrode conductors.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
you need the ground wire, 100%, no doubt about it. Why do these people think you dont need it?

I don't know when I ask they say are you in city limits?
I say no
Is the sub going to be a mobile home?
I say no
They say you don't need it Just put a ground rod at the new service.
I say, but I read it in a book to do it this way.
They say that it's been done this way for decade. just bond the new panel and unbond the old one :lol_hitti
And I will be using #4 for all the new grounding rods.
 

sammerdog

Banned
Joined
Jan 18, 2008
Messages
1,477
Location
West Michigan
Picture011-2.jpg

...what's with only two beers on the ground? Don't ya know when running electrical service, you should have at least THREE people there (you and TWO buddies). That way when you get electricuted, one can grab your ankles and one can grab your arms and drag you out front to the ambulance...
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
...what's with only two beers on the ground? Don't ya know when running electrical service, you should have at least THREE people there (you and TWO buddies). That way when you get electricuted, one can grab your ankles and one can grab your arms and drag you out front to the ambulance...

:spit: Those are cans of pvc glue.
Haven't had the outher kind of can in seventeen years two mouths and twentyone days. :lol_hitti
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I don't know when I ask they say are you in city limits?
I say no
Is the sub going to be a mobile home?
I say no
They say you don't need it Just put a ground rod at the new service.
I say, but I read it in a book to do it this way.
They say that it's been done this way for decade. just bond the new panel and unbond the old one :lol_hitti
And I will be using #4 for all the new grounding rods.

you arent in city limits, so your work needs to meet the 2008 NEC.

it used to be, that if you were feeding a detached structure, you could didnt need the ground. This is not the case anymore. This doesnt even apply do you since your garage is attached to the house.

If I were you, I would quit seeking electrical advise from whoever you have been talking to. Its obvious they are stuck in 1982, and are not doing you any favors.

I am concerned about the ability of that #8 to clear a fault. How long is it?
 
To avoid these ads, REGISTER NOW!

JeepsAreBuilt

Well-known member
Joined
Nov 24, 2006
Messages
1,066
Location
The Beautiful NorthWest
...what's with only two beers on the ground? Don't ya know when running electrical service, you should have at least THREE people there (you and TWO buddies). That way when you get electricuted, one can grab your ankles and one can grab your arms and drag you out front to the ambulance...

Well.. then whos gonna carry the beers ? :beer::lol_hitti
 

RoyB

Member
Joined
Sep 6, 2007
Messages
8
Location
Chicago Burbs.
how come you are putting a panel outside? I also cant believe that you guys can use pvc right into the panel like that! i would check to see if you need to ground the meter too. lot of different codes out in chicago depending on where you live, but some require the meter grounded as well....some villages like the ground rod through the meter and panel and all the way to the cold water pipe un-cut. also make sure you jump the water meter as well.

you guys have to ground the gas pipe too? thats new to me.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
how come you are putting a panel outside? I also cant believe that you guys can use pvc right into the panel like that! i would check to see if you need to ground the meter too. lot of different codes out in chicago depending on where you live, but some require the meter grounded as well....some villages like the ground rod through the meter and panel and all the way to the cold water pipe un-cut. also make sure you jump the water meter as well.

you guys have to ground the gas pipe too? thats new to me.

I was told that a feed though box that's 200 amp. cannot be inside. Their are alot of homes around here that have the breaker box outside with pvc.
I'm glad that it is because the 4/0AL. cable has to have the terminations outside. I learned that one the hard way.:lol_hitti

Oh and if you look in the pic. you can see I have the meter and the box set up for a ground. or I might have the collar on the wrong side.
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
I was told that a feed though box that's 200 amp. cannot be inside. Their are alot of homes around here that have the breaker box outside with pvc.
I'm glad that it is because the 4/0AL. cable has to have the terminations outside. I learned that one the hard way.:lol_hitti

Oh and if you look in the pic. you can see I have the meter and the box set up for a ground. or I might have the collar on the wrong side.

The ground rod is going to land on the grounding bushing??
 

RoyB

Member
Joined
Sep 6, 2007
Messages
8
Location
Chicago Burbs.
I was told that a feed though box that's 200 amp. cannot be inside. Their are alot of homes around here that have the breaker box outside with pvc.
I'm glad that it is because the 4/0AL. cable has to have the terminations outside. I learned that one the hard way.:lol_hitti

Oh and if you look in the pic. you can see I have the meter and the box set up for a ground. or I might have the collar on the wrong side.

I don't understand the point of the feed-thru box I guess. Where does it go from there, right to another panel inside the house? I see the ground bushing on the panel side....like I said, it depends on your village and what they require. I've even seen some require ground bushings on both sides of the feed.
 

RoyB

Member
Joined
Sep 6, 2007
Messages
8
Location
Chicago Burbs.
so why can't you just go from the meter to the panel inside the house? is it too far? or is that like a detached garage?
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
Ok it took me a little while to change it, but I think I got it the way you suggested. This is going to save me alot of money.:spit:


meterbypasss.jpg
[/QUOTE]
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I think I would of done that a little differently myself but your way will work just fine.

I would of left your 2" pvc stubbed up near the bottom of the meterbase with the expansion fitting on it. Let the power co. cut power, remove the mast and wiring, and plug the hole in the top of the meterbase. Stub your conduit into the bottom of it and reland your wires on the top of the meterbase and installed a meter jumper kit. Done. It would of saved you the cost of a j-box and those spendy insulated taps it looks like you're using.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
Thanks Aceman That would of been a better way :( But for some reason I though I would needed the old one some day. :headscrat
My neighbor has a transformer at the far conner of my place, and I was thinking of putting new barn with it's own power some day.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
thats crazy they energized it with that undersized ground, but glad you got it done and working.
 
OP
7

700jfm

Well-known member
Joined
Jan 29, 2008
Messages
383
thats crazy they energized it with that undersized ground, but glad you got it done and working.

I asked about the ground and he acknowledged that a ground wire is the new code in the city, but though it's a waste of wire :spit: And where I'm at not required. He knew of some inspectors before it was the "code" rejecting anyone who had one. So small wire or big wire, with wire or no wire, I'm going to live with it, or die with it. :thumbup:
 