How much voltage drop house wiring is too much?

In my office not far from the breaker box on a 15A circuit and 14ga wire I just checked and with no load it runs 121.5v. It's running 117v with a space heater on low and using 4.75A, with the heater on medium it's 116v using 7A and on high it's 112.5v using 11.2A although the last time I checked on high it was down to 110 point something.
 
To avoid these ads, REGISTER NOW!
OP
D

David0858

Well-known member
Joined
Oct 30, 2016
Messages
201
Location
Tx
5% is the nec recommended voltage drop so that would be 114v.

What else is on this circuit?

Not much as there's no voltage drop until I turn the heater is on at least low. Maybe a lamp, maybe a lamp and my computer (If it is it uses very little). The wiring is so squirrely I'm not sure what plugins in this room are on what breakers.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
That seems a bit much, I might be looking at connections too. These are the things I like to rewire and the best scene for a heater is a 12 wire, from breaker to outlet.
When I hear 14 wire I start thinking backstab.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,274
Location
Modesto, CA
Not much as there's no voltage drop until I turn the heater is on at least low. Maybe a lamp, maybe a lamp and my computer (If it is it uses very little). The wiring is so squirrely I'm not sure what plugins in this room are on what breakers.

how long is the wire run?
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
What is the voltage at the panel during the same time? Making sure the voltage drop is between the breaker and the outlet not the transformer and panel.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am not a fan of hooking heating on old general circuits. I use those heaters on occasion and I pretty much run a new wire for them on 20A. Eliminate as many old connections as I can, most of the time all of them. If this is your own home,,, which is likely since its 15A I would be tempted to run a new wire if its humanly possible.
Doubly true if you describe the wiring as "squirrelly".
 