How NOT To Hang A Ceiling Fan!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Had lunch in a local Moe's Southwest Grill. They have the typical, no ceiling, open to the roof sheet, structure exposed, ducts and conduit exposed, setup, all painted flat black.

Well, I started looking at the ceiling fans............. Tell me this is code somewhere........ anywhere............... NOT!!!!

4 in square box mounted to the bar joist, flat 4" cover plate with center knockout, 1/2 set screw type conduit fitting screwed in the knockout, about 3 ft of EMT to another 1/2 set screw conduit fitting screwed into an octagon box, to which the fan mount and ball socket is attached, then a 6" downrod to the fan.

If you look close at the 4" cover plate and set screw conduit fitting, there is a shiny spot where the fitting has loosened and walked in the knockout hole after the flat black paint was sprayed.

Charles
 

Attachments

  • how not to hang a ceiling fan.jpg
    how not to hang a ceiling fan.jpg
    125.6 KB · Views: 572
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
maybe there's a wire rope inside the conduit holding it all together :)
 
OP
C

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
maybe there's a wire rope inside the conduit holding it all together :)

Yea, I hope. But if they didn't have the forethought to use a long downrod, so do 'ya think....... Naaaaa! And I didn't get a pic of it, but this particular fan, the blade tips were passing within about 3 inches of a wall mounted television. Not sure what the TV's are for, I've never seen them turned on. They are older, heavy, CRT type.

Charles
 

ptschram

Well-known member
Joined
Sep 8, 2006
Messages
2,573
Location
Churubusco, IN
I am no longer the biggest nerd on the planet!

Thank you sir, I stand in awe.

No really, I'm the kinda guy who would do the same, maybe not take pics though.
 

burleymike

Well-known member
Joined
Feb 25, 2009
Messages
935
Location
SE Idaho
My wife always tells me to knock it off when we go out. I do the same thing, lets hope those wire nuts are tight because when the fan comes loose they will be holding the fan.
 
To avoid these ads, REGISTER NOW!

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
Not the frist time I have seen it.
What they are trying to avoid is the amount of sway you get with out of balance blades if you go to a real long down pipe.
The EMT fittings are a bit stiffer.
I don't know if the code even addresses this.
 
OP
C

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Not the frist time I have seen it.
What they are trying to avoid is the amount of sway you get with out of balance blades if you go to a real long down pipe.
The EMT fittings are a bit stiffer.
I don't know if the code even addresses this.

Code does not allow EMT or its system components to be used to support ANYTHING!

314.27(D) says that boxes used to support paddle fans must be specifically listed for the purpose (which I'm sure the standard 4" square box and cover are not, even though the octagon box may actually be a fan box, no way to tell from the floor). 358.12(5) appears to prevent EMT from being used to support luminaires or other equipment

Charles
 