I found a couple of coils of wire at my parents house while cleaning out some of my old junk from years ago and ran into a few questions.

1. Can the old style, white, 12-2 and 12-3 still be used today and still be code compliant. I know the gauge is OK for 20A put the color is the concern.

2. Is BX cable still used or is it better for copper scrap? I don't need to use it but wanted to see if it's worth selling or not.

Thank you.
 
To avoid these ads, REGISTER NOW!

mtne

Well-known member
Joined
Dec 3, 2007
Messages
113
Location
Denver
To the best of my awareness I don't thing there's any reason NOS 12/2 and 12/3 wouldn't be perfectly acceptable.

Spray paint the BX green and sell it for double........... :lol_hitti

.... umm, inside joke ......

The BX is likely just good for scrap.............
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,788
If it is 12 or 14 NM cable & not NM-B, it is scrap metal, as older NM cable fails 2008 NEC art 334.112 which requires 90 degree C insulation, older NM cable ( w/o the -B) is only 60 degree cable. If it is white 12/2 NM-B it's fine, there is no code requiring color coded NM cable.
 

mtne

Well-known member
Joined
Dec 3, 2007
Messages
113
Location
Denver
If it is 12 or 14 NM cable & not NM-B, it is scrap metal, as older NM cable fails 2008 NEC art 334.112 which requires 90 degree C insulation, older NM cable ( w/o the -B) is only 60 degree cable. If it is white 12/2 NM-B it's fine, there is no code requiring color coded NM cable.

Good catch Norcal! Thanks!
 
To avoid these ads, REGISTER NOW!

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
If it is 12 or 14 NM cable & not NM-B, it is scrap metal, as older NM cable fails 2008 NEC art 334.112 which requires 90 degree C insulation, older NM cable ( w/o the -B) is only 60 degree cable. If it is white 12/2 NM-B it's fine, there is no code requiring color coded NM cable.

Interesting - just finished up rough-in om a large addition, homeowner supplying all materials, and all 12-2 was yellow. End of the day, used up the last of the last 250' roll,and needed about 9 feet for a switch run. HO scrounged up a length that was black, was 12-2 w/g NM-B, so used it. Inspector failed the inspection - "couldn't read the lettering - replace it". Did so, as it's so much easier than fighting it. Funny part was the run went to a fan/light, and I had forgotten to plug an unused Knockout hole in the junction box, which he missed completely, and right there was the lettering plain as day, visible from the floor!
 

cderalow

Well-known member
Joined
Nov 13, 2011
Messages
1,326
Location
Potomac, MD
I recently used MC cable and really didn't know the difference between that and BX. Must be on the inside. Maybe BX didn't have a ground. You can't use flex cable as a ground.

correct. BX doesn't have a dedicated ground, or the paper sheathing
 