kegerator not cooling

jshua888

Member
Joined
Nov 26, 2018
Messages
11
Location
Las Vegas
Ive got an older dual kegerator that needs a freon refill. i dont trust myself to do it. any suggestions
 

Attachments

  • IMG_0413.jpg
    IMG_0413.jpg
    82.4 KB · Views: 27
To avoid these ads, REGISTER NOW!

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
are you sure it need Freon?
does the compressor run...evap fan running, condenser fan running----if yes my guess is a dirty condenser coil.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Not much to go on here, but my guess is it's a hermetic system. They usually don't have leaks unless somebody serviced it and used piecing valves and didn't braze in real service ports.

If it runs at all, I'd check the condenser coil for dirt and prove the condenser fan is running and running at speed. The chance of the evaporator being dirty is slim, but you would probably see ice buildup on it if it was dirty or there was a problem with the evaporator fan.
If it has auto defrost, the defrost timer may be stuck in the defrost cycle or has gone bad.

Tommy
 