For those of you with Kohler Generators equipped with Kohler automatic transfer switches. Specifically all versions of the Kohler RDT:
During the crazy storms in the past 2 weeks, one day we had Utility power go off and on about 10 times in as many minutes and drove the ATS controller crazy (they are programmed for follow a specific process in the start up, transfer, transfer back, cool down and shut down process. Evidently when they receive constant back to back conflicting conflicting commands, they just quit.
After the storms cleared I was left with a functional generator that would start if I set it to manual start, but the ATS would not send or maintain a start command.
I diagnosed the problem down to the controller card in the ATS. Kohler dealers wanted anywhere between $800 to $1050 for a replacement and days to weeks for delivery.
Spent some time searching around and found a company that not only repairs these cards for $275.00 + roundtrip freight, but also makes a new and improved model card for $375 that is much less likely to fail. I purchased the new and improved card and they shipped the same day I placed the order.
I installed it and it works perfectly. One thing to note is the card I received was jumpered to 50hz when of course anywhere in NA should be 60hz. Good thing I put the cards side by side before installing.
For those of you with Kohler RDT transfer switches, here is a good and inexpensive source for repairs and / or spares for the controller.
The Kohler Part # is GM35950L (I'm sure there are many variations of the letter designation)
Flight Systems Part # is 72-GM35950-00


During the crazy storms in the past 2 weeks, one day we had Utility power go off and on about 10 times in as many minutes and drove the ATS controller crazy (they are programmed for follow a specific process in the start up, transfer, transfer back, cool down and shut down process. Evidently when they receive constant back to back conflicting conflicting commands, they just quit.
After the storms cleared I was left with a functional generator that would start if I set it to manual start, but the ATS would not send or maintain a start command.
I diagnosed the problem down to the controller card in the ATS. Kohler dealers wanted anywhere between $800 to $1050 for a replacement and days to weeks for delivery.
Spent some time searching around and found a company that not only repairs these cards for $275.00 + roundtrip freight, but also makes a new and improved model card for $375 that is much less likely to fail. I purchased the new and improved card and they shipped the same day I placed the order.
I installed it and it works perfectly. One thing to note is the card I received was jumpered to 50hz when of course anywhere in NA should be 60hz. Good thing I put the cards side by side before installing.
For those of you with Kohler RDT transfer switches, here is a good and inexpensive source for repairs and / or spares for the controller.
The Kohler Part # is GM35950L (I'm sure there are many variations of the letter designation)
Flight Systems Part # is 72-GM35950-00