For Armoured MC cable - 8AWG to be more specific, does it fall into the 90 degree or 75 degree column by default. IE, NMB would make this 8AWG in the 60 degree column
330.80 Ampacity. The ampacity of Type MC cable shall be determined in accordance with 310.15 or 310.60 for 14 AWG and larger conductors and in accordance with Table
402.5 for 18 AWG and 16 AWG conductors. The installation shall not exceed the temperature ratings of terminations and equipment.
Derating aside, I always though 6 awg was for 50 amps...
I'm looking at a chart at it shows for 8 awg, 90 at 55 amps, and 75 at 50 amps
Here's the scoop. I plan to run a 50 amp for a electric car charger....
I already have some leftover 8/3 MC wire in my stash.
I also do have spools of 6 THHN, but if I can use up the 8/3 MC, I'd prefer to utilize this instead of the 6 wire.
Thoughts ?

http://www.encorewire.com/wp-content/uploads/EncoreWire-MC-PVC-AL.pdf
This is what I was referencing when I said the ~chart shows these ampacity ratings~
Here's the scoop. I plan to run a 50 amp for a electric car charger....
I already have some leftover 8/3 MC wire in my stash.
I also do have spools of 6 THHN, but if I can use up the 8/3 MC, I'd prefer to utilize this instead of the 6 wire.
Thoughts ?
Here's the scoop. I plan to run a 50 amp for a electric car charger....
I already have some leftover 8/3 MC wire in my stash