Hello,
Looking for some advice.
I have a utility pole with my meter main on it (square d sc816d200c) that I rigged up and the utility connected. This is where my service disconnect is. I then have a another homeline square D 80 circuit 40 space 200 amp panel that will serve all the needs within the home. I have run 2'' schedule 40 pvc conduit underground in under the house into the crawl space. Here is where I am curious:
Plan is to pull 4/0 4/0 4/0 2/0 (Hot/hot/neutral/ground) in through the conduit.
Does it matter if I use thwn vs xhhw? Or is there an alternative? Was looking at mobile home feeder wire but can't find 4 wire version locally.
I was thinking of terminating the thwn/xhhw wires in a juction box in the crawl space and converting to SER and run that through joists up to my panel (15-30 feet maybe). Other option is to keep the thwn/xhhw going all the way to the panel. Problem with that is it would seem obnoxious to run the conduit through the crawl space. Any thoughts or errors you see with my plan?
Looking for some advice.
I have a utility pole with my meter main on it (square d sc816d200c) that I rigged up and the utility connected. This is where my service disconnect is. I then have a another homeline square D 80 circuit 40 space 200 amp panel that will serve all the needs within the home. I have run 2'' schedule 40 pvc conduit underground in under the house into the crawl space. Here is where I am curious:
Plan is to pull 4/0 4/0 4/0 2/0 (Hot/hot/neutral/ground) in through the conduit.
Does it matter if I use thwn vs xhhw? Or is there an alternative? Was looking at mobile home feeder wire but can't find 4 wire version locally.
I was thinking of terminating the thwn/xhhw wires in a juction box in the crawl space and converting to SER and run that through joists up to my panel (15-30 feet maybe). Other option is to keep the thwn/xhhw going all the way to the panel. Problem with that is it would seem obnoxious to run the conduit through the crawl space. Any thoughts or errors you see with my plan?