MHF wire for RV 50A plug?

MarionV

New member
Joined
Nov 30, 2021
Messages
1
We are needing to get electricity to a RV. From our panel, the distance is 400'. On the other end, a simple 50A outlet will be installed to plug the RVs big extension cord into. The calculations I've done suggests either #2 Copper or #4Al. I have been reading about mobile home feeder wire (2-2-4-6)and that seems like the way to go. I especially like that option because we can direct bury it and save on the cost of PVC for 400'. Is a 50A breaker in the panel big enough to handle wire that big? Also, is this the best option for wire? Price wise is seems like the best option these days. I appreciate any advice on this job!
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Look up the breaker for your panel and see what it's rated for. I bet it will be a struggle. You could always connect to the breaker with a smaller piece of copper then transition to the MHF in a junction box outside the main panel

MHF is basically the cheapest option if you aren't running conduit. If you were, xhhw might be a little cheaper.

At 50a and 400', #2 will be a 5% voltage drop, which may not play well with some of your stuff. That said, if your actual draw is less, you are probably fine
 