Good afternoon. I have a Modine Hot Dawg 75AH0134 that is around 20 years old, that has never given us any problems, until recently. When there is a call for heat, the unit will go through its start up cycle, including energizing the heating element. No gas is released from the valve. The unit will cycle 5 times and then go into lockout. The valve will flash 6 times, indicating a lockout. The 2 rollout switches and the limit switches all are closed, showing 14 ish volts across them. I watched the low side of the transformer and see about 25 - 26 volts to the circuit board. The low side voltage is steady. The pressure switch also shows 14 volts. I expect 24 volts. I replaced the circuit board and have the same problem. I unplugged and jumped around the limit and roll outs. The venting is wide open. It’s hard to confirm, but I can only assume that the new board is transferring 24 volts to the valve. Also, I did purge the gas line, for fun.
Has anyone ran into this issue? After chasing the usual suspects, I’m now suspicious of the gas valve.
Thanks
Has anyone ran into this issue? After chasing the usual suspects, I’m now suspicious of the gas valve.
Thanks