Modine hotdawg conversion to gas.

ripsnortMN

Well-known member
Joined
Jan 26, 2009
Messages
1,160
Location
Mn
Hey guys. Have a modine hotdawg that I’ve ran on propane for the past 13 years. I’m in the middle of converting it to natural gas. I just did the gas conversion with the regulator spring swap and the three jet change. It has the Honeywell valve in it. Is there any other adjustment I need to make to the valve other than the spring swap?
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,854
Location
Fargo, ND
Once you get the gas hooked up and running you will need a manometer and check manifold gas pressure after the gas valve, and adjust that regulator spring you swapped out.
 
OP
R

ripsnortMN

Well-known member
Joined
Jan 26, 2009
Messages
1,160
Location
Mn
Does this absolutely need to be adjusted on this model? 45k btu modine hotdawg.
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,854
Location
Fargo, ND
Does this absolutely need to be adjusted on this model? 45k btu modine hotdawg.
Yes, on any new install or converted gas furnace/heater the gas pressure needs to be checked and adjusted.

I have found gas furnaces with burned out heat exchangers with the manifold pressure set nearly 2X recommended pressure. The hight gas pressure took out the heat exchanger. I have also seen furnaces with gas pressure half of what it is supposed to be set. Lower is usually not a problem as far as damaging the unit, but you will get half the output.
 
OP
R

ripsnortMN

Well-known member
Joined
Jan 26, 2009
Messages
1,160
Location
Mn
I just ordered a manometer so I’m going to try and do this myself.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,854
Location
Fargo, ND
2-3 feet of clear vinyl tubing and water with food coloring would do the same job with little expense.
 