Mr.Heater electrical issue

Paintphreak

Member
Joined
Mar 19, 2016
Messages
10
Hello, I've got a Mr heater MHU80 unit installed and ran for a few months earlier this year no problem, however I switched thermostat units from a simple 2 wire to a digital 4wire to run the fan during the summer. It ran fine for a night or so, then popped the 3amp fuse. I replaced it, but it keeps popping. Not sure whats wrong? The unit has the green ground hooked up thru the junction box on the back to the main electrical wiring for 110v, but was wondering if it may need a separate chassis ground? I tried going back to the 2wire thermostat, but same result, just keeps popping the 3amp. Now with the new fuse, and no matter the thermostat, it will blow the 3amp fuse as soon as I plug the unit in! Any help appreciated. Thx
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,884
Location
NW Iowa
How did you connect the new thermostat. I don't think unit heaters usually have a fan terminal.
 

sarman47

Well-known member
Joined
Aug 18, 2011
Messages
153
Location
Ontario, Canada
Here is what the manual has:

Link: https://www.mrheater.com/mwdownloads/download/link/id/30/

Sorry for the Caps, I copied and paste.

OPTIONAL THERMOSTAT INSTALLATION
IT IS RECOMMENDED TO USE 18AWG WIRE WHEN INSTALLING THE
THERMOSTAT. CONNECT ANALOG THERMOSTAT WIRING TO TERMINALS ‘R’ AND ‘W’ AS ILLUSTRATED ON THE SCHEMATIC DIAGRAM OR CONNECT A DIGITAL/WiFi THERMOSTAT TO ‘R’ ‘W’ ‘C’ AS ILLUSTRATED. NOTE: THERMOSTAT TERMINAL CONNECTIONS ARE MOUNTED ON THE BACK PANEL OF THE HEATER.
EXTERNAL THERMOSTAT TERMINAL STRIP WANING: DO NOT CONNECT LINE POWER TO THE THERMOSTAT TERMINAL STRIP.

To use the blower for air circulation only, your thermostat must have a “fan only” or fan selection setting. In case your thermostat has this option. an additional wire should be run to the “G” terminal on the thermostat connection block. See wiring schematic on page 13.
 
OP
P

Paintphreak

Member
Joined
Mar 19, 2016
Messages
10
Yes , I have the instructions, and wired with 18awg, can't figure out why it would keep blowing the 3aml fuse on the control board ?
 
To avoid these ads, REGISTER NOW!
OP
P

Paintphreak

Member
Joined
Mar 19, 2016
Messages
10
Yeh, just tried that, blew another fuse!? I'm not sure whats wrong unless something is wrong with the control board itself? Anybody experienced same thing? Lmkthx
 
OP
P

Paintphreak

Member
Joined
Mar 19, 2016
Messages
10
It was the foil on the sensor! Smh.... Thanks for all the input and special thanks to sarman47! ����
 

sarman47

Well-known member
Joined
Aug 18, 2011
Messages
153
Location
Ontario, Canada
Glade to hear it is all fixed. Sometimes it can be the smallest things. Here is to a toasty garage this winter............
 