New 40x50 metal sub panel install

Donniepowell

New member
Joined
Oct 9, 2012
Messages
2
First post but been lurkingfor a while. Well after several years I finally have my building going up tomorrow. I have the electric guys coming out but thought I would lean on you guys for some reassurance. I have read and searched numerous threads here and seems several opinions on wire to panel. I don't have access to mobile feeder wire and honestly don't want to wait on ordering it. It appears I am limited to copper and I am fine with that. Here is what I need to do

100a sub
Have space in panel for breaker
2 inch stub in concrete
Aprox 125 ft run to shop

2 options are
1- run from panel through attic to back side of house down the wall and trench to shop
2- run outside panel and bore under sidewalk and navigate septic to shop

Any suggestions of what would be more efficient.

Last question is wire size. Will thhn #4 for the 2 hots, #6 for the neutral and #8 for the ground work?

Great place here and have tons of ideas, just have to get the basics completed first. Electrical will start Friday.
 
To avoid these ads, REGISTER NOW!

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Not an expert, but I think you'd need at least three #2 for the hots and neutral and #4 for the ground, Might even need a bit larger due to the length of the run to account for line loss/voltage drop. This assumes you want to have the full 100A at the sub-panel.

As for your listed run path options, I'd vote for number one.

Hopefully some of the experts will chime in later...

Paul
 
To avoid these ads, REGISTER NOW!
OP
D

Donniepowell

New member
Joined
Oct 9, 2012
Messages
2
Thank you Paul, i am leaning toward that path. The other half is wanting it out of sight so it will take a little coaxing. I am curious to hear what the experts have to say for sure.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Option #1 would require you to run conduit all through the attic or run a cable instead and splice to individual conductors before it goes underground. Requires a j-box, splices(I like insulated taps myself, but not necessarily cheap) and a few more parts.

For that reason, I would go lean towards option #2 myself. It's a cleaner install, no extra splices, j-boxes, or different wire types.

But, does your panel outside have capabilities to add a breaker for feeding the shop?

If running copper you need #3, you could probably drop down to a #4 neutral without issues if you have some 240v load out there. #8 ground.
 