New Compressor 50-6P or? Help

NitroShark

Well-known member
Joined
Jan 8, 2010
Messages
518
Location
Greenville, SC
I’m replacing my 5hp 230V 1Ph compressor with a 7.5 hp model. My home shop already has (5) 240V 50-6R plug connection for other machines. I would like to keep this theme for the compressor but, in an industrial environment they are hard wired to a disconnect. This is a home shop.

Manual says 8-2 wire 35Amp beaker. I’d like to use a 6-2 wire 50Amp Breaker 50-6P plug.

Thoughts from my GJ Sparkys? Please help.


Thanks


attachment.php
 

Attachments

  • 7.5hpnp.jpg
    7.5hpnp.jpg
    43.1 KB · Views: 278
To avoid these ads, REGISTER NOW!

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
6-50 receptacle only rated for 3HP from what I have found. You just need to replace the 6-50 receptacle with a plate and run a whip to the compressor

As far as wire size and breaker if the manufacturer specifies it, it's what I would follow.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,322
Location
NJ
35A seems way too small. I wouldn't go smaller than 50A - it is a motor circuit once hard-wired, so you can be up 250% of FLC.

It the compressor is more than 50' from the panel and/or line of sight is blocked, then you need a disconnect local to the comp.
A disco also makes for a good transition to flexible wiring to the comp.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,931
Location
NW Iowa
35A seems way too small. I wouldn't go smaller than 50A - it is a motor circuit once hard-wired, so you can be up 250% of FLC.

For sure^

I'm a little curious about that nameplate. It shows a low voltage and high voltage wiring diagram typical of a 115/230v motor, but only lists 208-230 as operating voltage. It does have a slash after the 208-230/ like there was another voltage but they didn't list it. Weird:dunno:
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,322
Location
NJ
For sure^

I'm a little curious about that nameplate. It shows a low voltage and high voltage wiring diagram typical of a 115/230v motor, but only lists 208-230 as operating voltage. It does have a slash after the 208-230/ like there was another voltage but they didn't list it. Weird:dunno:

Maybe Waylead Motor Company saving buck. Only stock 1 n/p in house!
I'm sure UL and CSA didn't see that in the submitted product samples for testing.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,931
Location
NW Iowa
The weird thing is I think 230 is the LOW voltage. That would make 460v the high voltage, not real common in a 1 phase motor. Of course this is purely speculation so I might be way off.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,322
Location
NJ
The weird thing is I think 230 is the LOW voltage. That would make 460v the high voltage, not real common in a 1 phase motor. Of course this is purely speculation so I might be way off.

I've never seem a 460v single phase motor either and assumed it was just a single voltage motor with an incorrect n/p.
However, Waylead thinks otherwise...........

Screen Shot 01-22-18 at 11.11 PM.jpg

So I would agree, 230v is using the low voltage connections.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
I’m replacing my 5hp 230V 1Ph compressor with a 7.5 hp model. My home shop already has (5) 240V 50-6R plug connection for other machines. I would like to keep this theme for the compressor but, in an industrial environment they are hard wired to a disconnect. This is a home shop.

Manual says 8-2 wire 35Amp beaker. I’d like to use a 6-2 wire 50Amp Breaker 50-6P plug.

Thoughts from my GJ Sparkys? Please help.


Thanks


attachment.php

As has been said need to ditch the 6-50r because only good for about 3HP. The 5HP comp shouldve been hardwired.

The NEC requires 50a rated wired (FLC = 40a * 1.25 = 50a.)

8/2 NM is limited to 40a so that wont work. The manual is wrong...

Need #8 THWN in pipe or 6/2 NM-b....

Breaker can be max 100a. but a lower rated breaker should be fine.

A bigger issue here is whether your PoCo allows such a large motor and whether their transformer and primary supply can handle the in-rush of that beast. Many PoCos have HP limits....

what is the size of your main service and what loads do you have?

edit: correct nomenclature for nema outlets is 6-50 not 50-6...
 
Last edited:
OP
N

NitroShark

Well-known member
Joined
Jan 8, 2010
Messages
518
Location
Greenville, SC
Re: New Compressor 6-50P or? Help

Plan now is to run a 50 amp breaker with 6/2 to disconnect. I have some 6/4 SO cord I could use from the disconnect to the compressor or just get sealtite and 6 THHN I think I got that also.

House is all electric 400AMP (2-200amp sub panels in the home) with separate 125amp service to the home shop.

As for the motor, I’m an engineer with Baldor electric so if I need a motor you can guess what I’ll use if it gives me trouble.


Finally, what would you guy's recommend for a disconnect? I'm don't need a fusible one and the mag starter is able to turn it on/off. Don't really need lock/out tag/out either-got that at the sub panel if needed.


attachment.php


attachment.php


attachment.php


attachment.php
 

Attachments

  • IMG_1525.jpg
    IMG_1525.jpg
    67.9 KB · Views: 175
  • IMG_1528.jpg
    IMG_1528.jpg
    75.7 KB · Views: 173
  • IMG_1527.jpg
    IMG_1527.jpg
    85.5 KB · Views: 172
  • IMG_1526.jpg
    IMG_1526.jpg
    70.1 KB · Views: 174
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Re: New Compressor 6-50P or? Help

Plan now is to run a 50 amp breaker with 6/2 to disconnect. I have some 6/4 SO cord I could use from the disconnect to the compressor or just get sealtite and 6 THHN I think I got that also.

House is all electric 400AMP (2-200amp sub panels in the home) with separate 125amp service to the home shop.

As for the motor, I’m an engineer with Baldor electric so if I need a motor you can guess what I’ll use if it gives me trouble.


Finally, what would you guy's recommend for a disconnect? I'm don't need a fusible one and the mag starter is able to turn it on/off. Don't really need lock/out tag/out either-got that at the sub panel if needed.


attachment.php


attachment.php


attachment.php


attachment.php

IIRC Cordage is not to be used for permanent fixed in place equipment.

How far away is the panel from the compressor?

A disconnect is required only if the panel is more than 50' away and not within sight of the equipment.

If you do get a disconnect, make sure its HP rated and the rating is at least the same as the motor HP rating.

AC pullout disconnects are commonly used for this and some models at the big box stores are rated for 10HP...
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You got to love residential. Been building houses for 100 yrs with electric, 20 extra spaces in a new panel and new build, no way to reach in to route and connect an additional wire to it. All drywalled back in. I saw a 100, brand new in a garage, 20 spaces, 1 installed.
 
OP
N

NitroShark

Well-known member
Joined
Jan 8, 2010
Messages
518
Location
Greenville, SC
Got the compressor today. It appears that the switch for the magnetic starter is not in a very convenient location. Is it OK to leave the mag starter in the on position and switch power on off with either the disconnect(one with a circuit breaker ) or Maybe a disconnect with the lever.

I like to cut the power to my compressor when I leave at night.

You guys are a lot of help and I appreciate it thank you.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,931
Location
NW Iowa
I'd either move the current one or add a switch for the magnetic starter. That way all your switching is the coil rather than the full motor current.
 
OP
N

NitroShark

Well-known member
Joined
Jan 8, 2010
Messages
518
Location
Greenville, SC
I'd either move the current one or add a switch for the magnetic starter. That way all your switching is the coil rather than the full motor current.

Bert, I don't follow you.

The existing switch for the mag starter is what I was asking about. I would be cutting power on/off to it. (the coil)

Does that make sense?

Switch Picture below: (little red lever in first picture on top left -hard to see )

BendPak-V-Max-Elite-Air-Compressor-ASME-Features-WEB.jpg
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,322
Location
NJ
OP,
Bert is talking about interrupting the control circuit while you are talking about shutting off the power using the disconnect or panel cb. I would not want to exercise a disconnect or cb that often.

If you really feel the need to prevent starting, then I would add another switch in series with the existing PS on top of/next to the starter. Leave the PS lever up in the on position and forget about it.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,931
Location
NW Iowa
Bert, I don't follow you.

The existing switch for the mag starter is what I was asking about. I would be cutting power on/off to it. (the coil)

Does that make sense?

Switch Picture below: (little red lever in first picture on top left -hard to see )
[/IMG]

It sounded like you wanted to switch the power to the whole compressor, all 30+ amps, with a disconnect or breaker. Either of those will wear out with frequent, multiple times a week use.

I suggested wiring another switch, one that's in a better location, in series with the coil of the starter since it is only fractions of an amp. Let the motor starter handle the high current switching like it is designed for.

If that's what you have been planning all along great, my misunderstanding.
 
OP
N

NitroShark

Well-known member
Joined
Jan 8, 2010
Messages
518
Location
Greenville, SC
Thanks Bert. we are on the same page now.


After further looking at the pressure switch/ mag starter setup it appears the relay is manually activated.

Is there an easy way to convert it to an electronic push button type?


.

attachment.php


attachment.php
 

Attachments

  • CompSwitch.jpg
    CompSwitch.jpg
    68.6 KB · Views: 52
  • compstarter.jpg
    compstarter.jpg
    94.9 KB · Views: 54

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If it is charged up and hasn't lost pressure than the switch or breaker isn't stRting under load. I however have seen them work as switches for decades. I understand if it is going long time without use but if it's pumped it isn't going to start/run.