I am 1/2 way through the wiring in my new shop and want to get the welding outlet done. The only problem is, I don't have a 220v welder yet.
I know it's a 50a outlet, but what should I size the breaker/wire for? I know it's not rated at continuous load, but I'm not clear on the rules for sizing of wire.
I wouldn't go bigger than a Miller 212 at the absolute most.
Thanks in advance.
Steevo
43.49600, -112.04300
Run 8ga wire, and leave the breaker out for now, or buy a 50A breaker and hope that is what you end up needing.
Research all of the models you might purchase, to be sure whether any of them have a 4-wire plug (hot/hot/neut/gnd).
Some welders provide a 115v convenience receptacle on them, which needs the neutral wire. This would require 8/3 w/gnd.
More typical is 8/2 w/gnd, which is a commonly available NM (Romex style) cabing.
Norcal
This not necessarily true the 120V supply could be derived from the welder & not require a neutral w/ the supply conductors.
pattenp
Virginia - USA
Aceman
Eastern Oregon
I agree. It's just simpler to size the wire and breaker as a general purpose 50A outlet circuit and not get into reducing the wire size because of it being used for a welder.
I agree. I usually only mention the smaller wire size when people are saying you have to run fullsized wire or the poster wants to do it the cheapest way possible.
awdblazer
winnipeg, manitoba, canada
blk88gt
since you dont know the load (welder) you must wire it to the receptacle
50 amp 2 pole breaker
6/3 nmd90, nmwu, teck90 (or 6/2 if strictly 220 but 6/3 will probably be cheaper)
then the receptacle depends if it is 120/240 or 240
6-50r for 240 only
14-50r for 120/240
when i was pricing out cable for my garage subpanel ba robinson off of chevrier was the cheapest
Jbullfrog
Avoca, Iowa
I ran 4 - 8's when I ran my second 220 outlet. The extra one is there if I need it, but currentlyl not used. I have a 50amp on both sides of my shop and an extension cord that will reach to the center at either end.
Thruxton
Virginia
Generally I like to oversize things, but the manual for my Hobart 185 says not to oversize the breaker, as it protects the circuitry inside the welder. They spec'd a 20A breaker for the 240V circuit so that's what I used. Even if you oversize the wiring for future equipment I would stick with the recommended breaker size, FWIW.
Blk88GT
Manitoba
I should have specified a few more things:
a) I'm running in conduit
b) The run will be approx 75ft
I was leaning towards pulling #6.
Thanks for the input.
pattenp
Virginia - USA
Do you ever see wanting to use this outlet for something else at times such as a large space heater? If you do then use #6. If it is strictly for welder use only then use the #8 as suggested but clearly mark the outlet as "Welder Use Only".
hh76
NE Wisconsin
If you are running conduit, you can always hold off on pulling wire until you have a welder. If you want to run it now, I'd suggest 6, just in case you find something else that would enjoy 240v, or decide on a bigger welder.
Norcal
8 AWG THHN is rated for 50A, more then adequate for most needs.