He miss figured the hole size.Finally got a reply from the duct manufacturer.
They are not HVAC duct designers but just build to the customers specifications.
After doing some rethinking , I think (dangerous i know) that I only want 1000 to 1200 cfm on the main duct running the shop length. The other 400 cfm I would branch off the AH left and right at around 200 cfm each side. That would get me some air under the loft area that will be built later.
They recommend a 16" duct with two rows of 3" holes every 24 ". So for 50ft that would give me 48 or 50 , 3" holes. If I did the mathe correctly that would be a total of around 353 sq in.
The 16" duct would be around 200 sq in.
He said by doing it as described above would give some velocity out of the holes.
I suppose that means more forceful air coming from the holes?
Does this sound like a good plan?
He revised the hole size to 2.25" at 24" o.c. which will give me 48 holes. At close to 4 square in. per hole will be a total of 192 square in. .
The 16" duct is 201 square in. on it's cross section.
So he's thinking being less outlet than input will give some force/velocity from the holes.
Just thinking in layman's terms, it makes sense now. I visualize it as putting your thumb over the end of the water hose to provide a little back pressure and get it to shoot farther out.
Any thoughts on this?
Thanks