Gents,
Need some help with this one. Currently have a 100A service, and looking to put in a 60A sub in the garage for my new millermatic 251 and syncrowave.
Current setup:
1) 100A house panel (full) - service is 3C/#3.
2) 60A sub panel in the basement which was used to feed a hot tub that not longer exists and now feeds the range and A/C.
Loads of concern: Range, Dryer, A/C, Jetted Tub (currently on a 2 pole 15), Hot Water Heater, Dishwasher and Microwave.
House Sqft: 2300 + 900 basement.
Here's the kicker, nothing really gets used that much. It's my wife and 4 year old daughter. A/C barely gets run, and only feeds the upstairs bedrooms. Furnace is gas, range never uses the full wattage. The reality is the most commonly used item is the dryer.
What I'm hoping to do is pull the dryer breaker, put a 60A in there and run a sub panel into my shop with 3C/#6 NMD (it's like 12ft) and then run the dryer off that panel, as well as my welders.
How's that sound? I've got a quote with the service provider to see how much it is to go up to 200A and just run a dedicated 100A panel in the garage but I'm not holding my breath as we are 100% underground service. And this is Canada!
(Attached pic is current setup)
Need some help with this one. Currently have a 100A service, and looking to put in a 60A sub in the garage for my new millermatic 251 and syncrowave.
Current setup:
1) 100A house panel (full) - service is 3C/#3.
2) 60A sub panel in the basement which was used to feed a hot tub that not longer exists and now feeds the range and A/C.
Loads of concern: Range, Dryer, A/C, Jetted Tub (currently on a 2 pole 15), Hot Water Heater, Dishwasher and Microwave.
House Sqft: 2300 + 900 basement.
Here's the kicker, nothing really gets used that much. It's my wife and 4 year old daughter. A/C barely gets run, and only feeds the upstairs bedrooms. Furnace is gas, range never uses the full wattage. The reality is the most commonly used item is the dryer.
What I'm hoping to do is pull the dryer breaker, put a 60A in there and run a sub panel into my shop with 3C/#6 NMD (it's like 12ft) and then run the dryer off that panel, as well as my welders.
How's that sound? I've got a quote with the service provider to see how much it is to go up to 200A and just run a dedicated 100A panel in the garage but I'm not holding my breath as we are 100% underground service. And this is Canada!
(Attached pic is current setup)

And you're asking whether you can add an additional 60A subpanel?