Propane supply to detached garage

BrianS

Well-known member
Joined
Jan 2, 2006
Messages
81
Location
Dayton, OH
I have a 100 gal propane tank buried behind my detached garage. It feeds the main house via a first stage regulator into 3/8" copper tubing to a Fisher R622 second stage regulator, then into 3/4" black iron pipe. I'm only running a cooktop and my grill on propane at the house.

I plan to add heat to my detached garage, looking at a 60-70k BTU furnace. My plan is to tee off after the first stage regulator, run 3/8" copper tubing to another Fisher R622 regulator at the garage, then 1/2" black iron for the heater.

Does this sound like a reasonable plan?
 
To avoid these ads, REGISTER NOW!

Adk Mike

Well-known member
Joined
Jan 13, 2014
Messages
331
Location
upstate NY
1/2 copper line running off a twin stage regulator from that tank to the heater will run 93,000 Btu’s in 10 feet.
So tap off the first stage and mound a 2d stage on the building if it’s farther than 10 feet.
Inside can be 1/2 pipe for a long ways. I size these every day.
 
OP
B

BrianS

Well-known member
Joined
Jan 2, 2006
Messages
81
Location
Dayton, OH
1/2 copper line running off a twin stage regulator from that tank to the heater will run 93,000 Btu’s in 10 feet.
So tap off the first stage and mound a 2d stage on the building if it’s farther than 10 feet.
Inside can be 1/2 pipe for a long ways. I size these every day.

Great info, thanks. It is much closer for me to come off the first stage at the tank than to come off the 2nd stage at the house (and it would be much farther than 10 feet). Going to tee off the first stage and mount another regulator at the garage.
 

Mainiac Mat

Well-known member
Joined
Sep 2, 2020
Messages
409
Location
Maine
There are tables in the Hot Dawg installation instructions that have the pipe size and flow rate tables. Just make sure you read carefully as the one table is for NG and has a correction factor for use with LPG. You can download the manual if you haven't sourced the heater yet.

I just put a 60K unit it and did so exactly as Adk Mike described, except my tanks are above ground and just on the other side of the wall from where the heater is.

T off the 1st stage regulater. 1/2" burried PVC to the second stage regulator on the house. 1/2" PVC clad copper to the second stage regulator on the garage.

Life is good.
 

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
Contact propane supplier and avoid any guess work.


Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
B

BrianS

Well-known member
Joined
Jan 2, 2006
Messages
81
Location
Dayton, OH
I went with 1/2" OD copper tubing after the first stage regulator to a new second stage regulator at the garage, then 1/2" black iron into the building.

Can anyone tell me what the grounding requirements are for this setup? At the house there is a grounding clamp on the pipe outside the building to a wire running into the ground. I assume I need something similar at the garage? Do I need to ground the pipe inside the building as well?
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Are you sure it's only a 100g tank ... never heard of one buried ?

FYI -- my studio w/ 38k heater had twin 100's above ground and in PA I had to get them filled (topped up) more then once during the winter. a single 100 is not holding much fuel at max 80% fill and refill at 20%.

I just had a full system installed ---1000g tank and many lines .... the wire was for tracing the pipe in the future
 
OP
B

BrianS

Well-known member
Joined
Jan 2, 2006
Messages
81
Location
Dayton, OH
Yes, I'm sure it is only 100g. The house only uses propane for the cooktop and grill and the covenants required it be buried.

Now I'm wondering if propane is the right way to go. I don't want to refill multiple times per year, once would be ok.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Yes, I'm sure it is only 100g. The house only uses propane for the cooktop and grill and the covenants required it be buried.

Now I'm wondering if propane is the right way to go. I don't want to refill multiple times per year, once would be ok.



100gallon tank can only be filled to 80 gallons -- and you should call for refill at 20gallons. So you have 60 gallons to work with. My guess -- not enough storage


How big is the building ? Do you rent the tank? I assume you own it rentals don't let you touch.
 
Last edited: