New to the forum. I currently have a 2 post lift (240v 20a) and I'm planning to add a new 4 post (120v 30a). Can I wire both to a single 240v circuit, 30a 2 pole breaker and #10 wire?
I understand the MWBC... but can he use a 30A breaker on a motor that calls for a 20A breaker? Knowing the individual motor horsepowers / current ratings would help the determination.
Brian
The breaker does not really protect the wiring, the applied load does. The breaker provides short circuit interruption.
Run 10-3, or (perhaps 8awg in conduit, like I did) to a sub panel near the lift, then pull two fused switches off that sub panel, one 240 v ( I think my lift called for a 25 amp fused disconnect) and one 120v appropriately fused switch for the four poster.