Quick NEC question

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,641
I need to run a 15amp 240v circuit to power a thru-the-wall AC unit in my garage. I'm considering using 2 conductor #14 romex and remarking the white conductor because I have it on hand. I seem to recall a conductor smaller then #6 cannot be remarked as per the NEC. Is this correct? Thanks.
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I think you are thinking of 200.6 but that only applies to "insulated, grounded conductors" (ie. neutral) You can take a white wire in Romex and remark it as a hot wire, its done all the time. You are not allowed to take a black or red and remark it as a grounded conductor (neutral). You cannot take a loose wire in conduit and remark the ends of it, in conduit it has to be marked full length. Romex is different.

Charles
 

VHF

Well-known member
Joined
Oct 27, 2008
Messages
420
Location
NW Wisconsin
Individual wires that size cannot be remarked, but I belive it is OK to remark conductors in a manufactured cable assembly such as Romex. For example, 10-2 Romex is frequently used to supply an electric water heater with the white wire remarked as red.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
the rule for #6 and smaller is for remarking black to white, and that doesnt apply to cable just individual conductors. Youre fine with your 14/2 as long as the AC unit doesnt need a neutral for some reason.
 