Recommendations heat pump wiring

rmeade

New member
Joined
Sep 13, 2023
Messages
3
Greetings!

I plan to install a 1 Ton (12,000 BTU) heat pump. I want to install wiring now and install the heat pump later (work on the panel is required). I want to install the wiring now because the roof is open (to this one story cottage)- making the task easy. Heat pumps in this size seem to be either 115v 15amp current (25amp breaker recommended) or a 230volt 10 amp current (15 amp breaker recommended).

What sort of wiring would be recommended for the 115volt system (10 or 12 gage, three wire) and, alternately what would be recommended for the 230 volt system (12 gage 4 wire)? MrCool equipment seems attractive (4th generation, Energy Star Ductless Mini-Split: DIY-12-HP-WM-115C25) although there is a lot of other manufacturers that are also attractive.

Thanks for your help!
 
Last edited:
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,172
Location
NJ
Here is the chart from the manual. You need to wire to the Minimum Circuit Ampacity (MCA) spec'd by the mfr.
Use the mca values and ignore their wire sizes as somebody missed the boat for wire sizing.
(How could 19A require #12 and 18A require #10, etc......) You should be fine with 12-2, 10-2 if it makes you feel better. Get a 240vac unit.
1694672837941.png
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
8,031
Location
In the only town in Pennsylvania, Bloomsburg.
To add...
Maximum current of a 12k unit is usually around 12 amps. Minisplits might run at maximum until the desired temp is achieved, then use less, much less (unless under rated). A #12 is sufficient for all but the longest wire runs at 9k/12k. If uindoubt as to the capacity that will be installed later, possibly an 18k?, then prewire a #10.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
My 2.5 ton units are on 12/2 nm-b with 25a breakers. That's probably what i would run in this case

Run 10/2 if you feel better
 
To avoid these ads, REGISTER NOW!
OP
R

rmeade

New member
Joined
Sep 13, 2023
Messages
3
Thanks for the replies.
MM0882: Why do you recommend the 240volt unit, So it looks like the 12nm-b would work there as well?

1694704238484.png
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,172
Location
NJ
Anytime I have the option of 240v, I would run it for usually a smaller wire size, lower voltage drop, allows for a longer length run without needing to upsize and possibly reduced light flicker to the rest of the home.

240v doesn't change the wire/cable required other than possibly smaller a size required. All power wiring is rated at least 300v and more predominantly at 600v.

These instructions are scary. Never heard of a "N" (nuetral) referred to as "Null". Maybe consider another mfr. What else is half-assed?
 