Running "Romex" behind crown moulding

JamieK

Well-known member
Joined
Aug 13, 2009
Messages
1,760
Location
Winston-Salem, NC
I'm going to be putting some new light circuits in my garage, but the walls have already been finished in drywall. There is no access to the ceiling over the garage. Can I fish the wire from the fixture through the ceiling joists, then drop down out of the ceiling where the wall and ceiling meet. Then run the wire in that upper corner over to the other side of the room and then run the wire back behind the wall down to the switch? Then cover the exposed wire with crown molding? Is that up to code or not?
 
Last edited by a moderator:
To avoid these ads, REGISTER NOW!

hammlm

Well-known member
Joined
Jun 21, 2005
Messages
684
Location
SE PA
Re: Running "Romex" behind crwon moulding

I'm not sure of code, but to be sure, you could run MC ("flex") in the manner you described.

Code or not, I would be very worried about an errant finishing nail finding its way into the NM-B cable.

You must have some garage if you're going to finish it with crown!!!

Let us know what you decide.
 

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
Re: Running "Romex" behind crwon moulding

I would still consider that exposed wire, which code would say needs to be in conduit.
 

uncletater

Well-known member
Joined
Oct 6, 2011
Messages
500
Location
China Grove, NC
Re: Running "Romex" behind crwon moulding

I agree it would not be a good idea. Nails may cause an issue if you hit the wire.

I do like crown in a garage. I think it makes it look more finished.
 

Attachments

  • DSC01567.jpg
    DSC01567.jpg
    145.3 KB · Views: 59
  • DSC01569.jpg
    DSC01569.jpg
    149.3 KB · Views: 67

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Re: Running "Romex" behind crwon moulding

Since the NEC specifies when running NM through bored hole or along the side of studs that the cable must be kept at least 1.25" back from nailing surfaces. I think running NM behind crown molding does not meet that distance requirement from a nailing surface.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
Re: Running "Romex" behind crwon moulding

why is there no access to the garage ceiling? if you have the space above there i would cut in an access hole and get up there.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Re: Running "Romex" behind crwon moulding

Talk to your inspector, because even though it is not to code to run on outside of Sheetrock they will let you staple it in the top corner most of the time. I've done it where the top was exposed like you said without crown molding and then anything down the walls snaked in. I've never had an inspector fail me for that. Now if it was in the middle of the wall where it could be damaged easy then either pipe or bx cable would have to be ran. I'm sure I will have someone comment on this saying I'm stupid and the only one ever to do it but I've seen it and done it plenty of times in garages and passed inspection.
 

gc427

Well-known member
Joined
Aug 7, 2009
Messages
263
Location
Glendale, AZ
Re: Running "Romex" behind crwon moulding

Nope.

Time to learn how to cut, patch and texture the holes you are going to be cutting in your drywall.

If it is going to be exposed it needs to be in flex conduit or EMT.

No PVC for air line plumbing either :lol_hitti
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Re: Running "Romex" behind crwon moulding

It's up to you but I would call the inspector first and ask,you might be surprised.
 

frankush

Well-known member
Joined
Oct 23, 2011
Messages
1,156
Location
IL
Re: Running "Romex" behind crwon moulding

In this area, armored cable is run behind baseboard quarter round all the time.
If it's remodeling work, I'd go for it with armored cable. Calling the AHJ is just going to open a can of worms.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Re: Running "Romex" behind crwon moulding

Just to give you an idea, I just did a 20kw generator with aluminum cable and romex for the control wires, I ran all the wires in the top corner above the garage door as I've done many times over the years,all passed with no issues. The only thing I ever have to do extra is fire stop the holes if I go I through the wall. I can't say about where you are but in nj there's no issues with the wires up high in the garage.
 

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
Re: Running "Romex" behind crwon moulding

The code actually specifies "protected from damage" for exposed wiring (NM). Let's not forget all the unfinished basement spaces that have "exposed" wiring.

Not sure I would agree with pattenp's interpretation of the code. I do not believe a bored hole is the same as wire behind molding. If you anchor the NM as required by the code and then cover it with molding (desperately trying not to damage it) you should be fine.
 

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
Re: Running "Romex" behind crwon moulding

Our code, which references the NEC, requires that wires within 1 3/8 inches of the surface be protected by metal plates or an equivalent nail and screw proof cover.
 