Rv outlet, how long before derating
signcrafter
Going to be adding a 30 amp 110 RV outlet either on the outside or inside of the garage for our travel trailer. This will be about 60 to 65 feet from the sub panel in the garage by the time I go up and over and back down. Is 10-2 romex good enough or do I need to derate for that distance? I have lots of 10-2 romex so hoping that will work and wont have to buy 8-2 since I'm guessing that will add up fast. But also want to do it right. Thanks
Shiftless
East Bay SFO
I calculated a bit more than 3% voltage drop if your RV is drawing your full 30 amps. (125 volts) Most of the time I suppose you will be using a fraction of that amount. You’ll be fine.
dcg9381
Austin, TX
Suggestion:
I dunno your full use case, but these days I run 10/3 to a 14-50R (Standard 50A RV outlet) on a 30A breaker. I put a label of "30A @240V" on the plate. This gives you twice as much available power if you're ever landing 50A RVs at your place or need to run a welder. 50A RVs really don't need 50A unless they are 3 or 4 AC "monster class" RVs.
You use the standard 50A to 30A adapter that I'm sure you already have to plug in your RV.
signcrafter
Suggestion:
I kind of like this idea. I would like a 50 amp outlet in case friends stay over with there camper. But is this code compliant?
dcg9381
Austin, TX
I'll let someone else answer that. I don't know of any prohibition for using a 50A receptacle on a 30A circuit with an appropriate breaker. I've seen some comments that the outlet itself is (perhaps) misleading, which is why I put a label on it. I "believe" this is allowed with a single breaker / single outlet scenario. The sparkies will know better than me. I believe it's covered under NEC 210.21(B)(1) - it's allowed as it's a non-branch circuit, so you can't overload it without tripping the breaker.
Bert_
NW Iowa
Suggestion:
It technically a code violation but it's really a good option and I have done exactly that before.
If someone wants to argue a safety concern I would ask how it's different than plugging a 50A adapter into a standard 30A RV outlet
Norcal
It's not "technically" a code violation, is flat out a code violation, a 50A receptacle is only permitted to have 40A or 50A overcurrent protection, but the worst that can happen is the breaker trips, which in the annoyance category. The problem is the 50A to 30A adapters, and 30A to 20A adapters, none of them are listed for good reason.
dcg9381
Austin, TX
Can you guys cite code on where it's a violation? It has to be expressly prohibited. NEC 210.21(B)(1) is a branch circuit deal. If it's not prohibited, it's allowed.
I'd claim the danger is the opposite, using a 50A adapter on a 50A protected 14-50R to go down to a 30A RV outlet, which is pretty common in the RV space. You'd smoke wires before tripping a breaker.
Bert_
NW Iowa
Yes the code says 40 can use a 50A receptacle. Why is a 40A circuit OK but a 30 is not? If there is a safety issue why not require 40A receptacles? No doubt the industry could make one.
I use the word technically to mean it is a code violation but not a safety issue. The original intent of the code is to cover safety not design issues.
Stuff
Which code section do you see that in? NEC states "A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit." The verbiage about 40 and 50 amp circuits and the receptacle table is for multiple-outlet branch circuits.
Bert_
NW Iowa
I checked my codebook and what I thought would not allow this installation, 210.21(B)(3), applies to circuits with (2) or more receptacles. A circuit with a single receptacle would not apply. I can't find anything else on the subject.
Unless someone else has something I am going to say a single 50A receptacle on a 30A circuit is code compliant
I have done this exact install before and assumed it did not meet code, but apparently it was fine all along!
Norcal
See table 210.21(B)(3). But as I wrote the worst that can happen is a tripped breaker, not like putting a 15A on a 50A circuit which is bad.
Stuff
That table is only used for 210.21(B)(3) - "Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3)"
The 2023 NEC clarified this by updating the table's title.
Bert_
NW Iowa
I thought that at first too. The table is for (2) or more receptacles.
dcg9381
Austin, TX
Again, I argue, "where is this prohibited"?
In the context of NEC, if it's not prohibited, it's allowed.
I'm not arguing that it's "smart" but a 50A rated receptacle on a 30A breaker is at worst going to be "confusing" (despite my 30A label on it) but it's not unsafe or unreasonable.
The number of worn out RV plugs I've seen astounds me. There are so many RV parks running under voltage or just that have worn out plugs.. I'd rather run 50A rated plugs and pull 1/4 of their rated output, seems "not dumb" to me.
dcg9381
Austin, TX
Why argue when I agreed with you in multiple posts?
Apologies, not speaking to you directly. Speaking to those that say it's a "violation". Requesting citation of violation (politely) - just like I'd do with any local code inspector who is dead *** wrong. :)
FredWanaker
NorCal
here any electrical cable to a trailer in a yard or at the street is the code violation. You can run one to charge the battery but it can't be an overnight thing.
signcrafter
HOA rules? I could see some codes to keep people from living in campers. But I use mine for when cleaning it before and after a trip. A lot of times its 80 to 90 degrees so being in it without AC on is cruel. Also will turn the fridge on to get it cooled down since it takes a while to get it to temp after being off. We do get guests every so often that will stay in there for 2 to 3 nights also.