SO and SJO cable

alan camby

Well-known member
Joined
Dec 3, 2011
Messages
1,566
Location
South of Indianapolis, Indiana
Is it ever ok to use as a permanent installation. I have seen factories come out of a j box and down jack chain to lights with so cable.

Is there a reason for a homeowner to use SO over SJO. I know the J means junior (300volt).

I saved $10 by buying SJO.
Was going to use a very short section for a 4000watt ceiling heater but see that the package for wire shows non permanent only. I need a disconnect or plug due to the distance from breaker box. If I can't use the SJO. Is hard wiring my only choice?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,793
Location
Long Island
Is it ever ok to use as a permanent installation. I have seen factories come out of a j box and down jack chain to lights with so cable.

Is there a reason for a homeowner to use SO over SJO. I know the J means junior (300volt).

I saved $10 by buying SJO.
Was going to use a very short section for a 4000watt ceiling heater but see that the package for wire shows non permanent only. I need a disconnect or plug due to the distance from breaker box. If I can't use the SJO. Is hard wiring my only choice?

Downstream of the disconnect IS non permanent. You're fine there.

If you've only got 120V or 240V, the J is fine, though SO has a thicker jacket. You shouldn't be subjecting the cord to damage anyway, so either is fine.

Just make sure you derate the circuit for constant heating use.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Flexible cord cannot be used in place of perm. wiring, either use a plug on one end or better yet sealtite.
 