Split 30A 220V into 2 20A 110V Circuits?

pparrett

New member
Joined
Jul 1, 2010
Messages
4
I'm fairly certain this can be done but I want to make sure I go about it the safest way.

I have a single 30A 220V 10Ga line going from my main panel to my detached garage (Red, Black, White, GND). I would like to have two separate 110V lines without adding another panel in the garage.

Could I replace the main panel breaker with two 20A breakers and then connect one circuit to each hot lines and share the neutral in the garage? Would I still use all 20A wire and outlets in the garage for each of the two circuits? I this correct for a multiwire branch circuit?

Any tips from electricians to keep this "code" would be great!

Thanks!
 

Attachments

  • 710ecmCQfig1.jpg
    710ecmCQfig1.jpg
    45.9 KB · Views: 86
  • 183911.jpg
    183911.jpg
    39.1 KB · Views: 80
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Since you have the four required wires, I would use the 240v circuit to power a small subpanel located in the garage, and simply tap off the subpanel with whatever you needed. In fact, now that I look and you say it is DETACHED, this is the only way to do this. You are only allowed to have one circuit supplying a building. You cannot have multiple circuits going to a detached building.

Charles
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Since you have the four required wires, I would use the 240v circuit to power a small subpanel located in the garage, and simply tap off the subpanel with whatever you needed. In fact, now that I look and you say it is DETACHED, this is the only way to do this. You are only allowed to have one circuit supplying a building. You cannot have multiple circuits going to a detached building.

Charles

he would be ok with what he is describing. MWBC is considered one circuit. The two 20 amps breakers need a handle tie (but they do anyways) if he installs a subpanel at the garage, hes going to have to install grounding electrodes, and isnt there a limitation where a 30 amp fed subpanel can only have two branch circuits in it?
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I'm fairly certain this can be done but I want to make sure I go about it the safest way.

I have a single 30A 220V 10Ga line going from my main panel to my detached garage (Red, Black, White, GND). I would like to have two separate 110V lines without adding another panel in the garage.

Could I replace the main panel breaker with two 20A breakers and then connect one circuit to each hot lines and share the neutral in the garage? Would I still use all 20A wire and outlets in the garage for each of the two circuits? I this correct for a multiwire branch circuit?

Any tips from electricians to keep this "code" would be great!

Thanks!

Use a 2 pole 20 amp breaker and you're fine. You also need a disconnect out there as well, the easiest solution would be a 2 pole snap(toggle) switch. Take your number 10's right into the switch as soon as they enter the building. Nothing to it.
 

Dan0myte

Well-known member
Joined
Nov 18, 2009
Messages
92
Location
Regina, Saskatchewan
Like Aceman said, no need for a subpanel if you're just doing a couple of simple outlets.

Just downgrade the breaker inside the house to 20A 220V, then run the one branch to one set of plugs and the other branch to the other set of plugs. Very simple and cost effective.
 

Daniel Dudley

Well-known member
Joined
Sep 4, 2009
Messages
3,546
Subpanels are pretty darned cheap. As cheap as a disconnect. If you ever wanted to upgrade the wire from the house you would be good to go in the garage.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Like Aceman said, no need for a subpanel if you're just doing a couple of simple outlets.

Just downgrade the breaker inside the house to 20A 220V, then run the one branch to one set of plugs and the other branch to the other set of plugs. Very simple and cost effective.

Not a problem on this side of the border,however it appears that there are several different interpretations of the NEC by the varying responses in this thread.As always,your local rules may vary...
 