Does anyone know if the split systems can be installed inside a ceiling pointing down.
My issue is my home is a colonial and it is finished.. There is zero access to the first floor to install central ac, the cellar has a finished ceiling.
The attic is open
My question is can I put the reciever in between the rafters in the attic in a hall way aiming towards the floor. My issue is I don't want to hang a unit on my wall.
trying to be creative
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Dude, they sell ceiling cassetes that are made to fit between joists. They look sorta like a ceiling AC unit in a travel trailer. All the majors make them. They also make ducted minisplits if you only want to see "normal" duct grilles.

I too hate the ghetto look of the standard wall units. I may grow to love them but anybody visiting my home will think it looks stupid.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
My question is can I put the reciever in between the rafters in the attic in a hall way aiming towards the floor. My issue is I don't want to hang a unit on my wall.
trying to be creative

Putting a heater in a hallway will easily heat the hallway. To heat the living space you would be much better off putting the indoor unit in the living space. Imagine that heater cycling on and off every time the hallway reaches setpoint.

I say heating but cooling is the same thing.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,100
Location
SE MI
Putting a air handler in a hallway will easily heat/cool the hallway. To heat the living space you would be much better off putting the indoor unit in the living space. Imagine that heater cycling on and off every time the hallway reaches setpoint.

They also sell units that are suspended from the ceiling, but they would have the same problem as just mentioned Ceiling Mounted Heat Pump

Better yet, you could get 2 of these air handlers, mount one at each end of the hall, pointing in opposite directions.
 
OP
S

SHELCO

Well-known member
Joined
May 25, 2006
Messages
73
Location
Medford Mass
As usual, I should have given more detail. When you walk u p the steps thre is a small landing with bathroom infront of you, bedroom to left and 2 bedrooms to right,

The air handlers are excatly what i need..thinking one in master bedroom and one in the other ''larger bedroom'' that will take care of the upstairs. 2 catridges off of 1 slim line?

Then I can purchase another unit for downstairs jus o take th edge off..
Thanks guys
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I've said this before-
Cassette units are problematic at best. They have very poor air flow, they sometimes drip condensation, the blower motor capacitors go bad & it requires taking almost the entire unit apart to get the electrical panel out to replace them.

Tommy
 
To avoid these ads, REGISTER NOW!

KoRNTERA

Member
Joined
Feb 23, 2014
Messages
11
It can be done with the proper compressor. Some will even go as high as 4.

You can actually go to 8 indoor wall heads or ducted slim air handlers or ceiling cassettes off one outdoor compressor bearing unit. Mitsubishi makes a 2,3,4,5,8 port outdoor heat pump and Daikin makes a 2,3,4,8 port system as well. In a commercial setting the possibilities are endless, my company just completed a 4 story building with 89 wall heads off a 60 ton outdoor Mitsubishi city multi heat pump
 
OP
S

SHELCO

Well-known member
Joined
May 25, 2006
Messages
73
Location
Medford Mass
Do I have to run a drip line from the heads? That would be a ton of work. You mentioned they leak, would that be the condensation
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
Do I have to run a drip line from the heads? That would be a ton of work. You mentioned they leak, would that be the condensation

For the ceiling units, you need a condensate pump.

For the wall units, it's a gravity drain, unless you 'need' a condensate pump.

And yes, the dripping is condensate.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
The cassette units are more difficult to service, but If you have good access from above you will be ok. I think the cassettes have a built-in condensate pump. You can block off up to two sides on them also, so you can make it a 2, 3 or 4 way blow. As far as the mini pumps go I have had good luck with the Aspen and Saurermann. I'm with Pseudo on preferring the high wall to cassettes.

I would suggest you buy a dual unit for the upstairs and a high efficiency single for downstairs. The cost of the dual vs triple is substantial. I bought the 16 seer dual for upstairs and a 25 seer unit for downstairs at very nearly the same price as a triple
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
The cassette units are more difficult to service, but If you have good access from above you will be ok. I think the cassettes have a built-in condensate pump. You can block off up to two sides on them also, so you can make it a 2, 3 or 4 way blow. As far as the mini pumps go I have had good luck with the Aspen and Saurermann. I'm with Pseudo on preferring the high wall to cassettes.

I would suggest you buy a dual unit for the upstairs and a high efficiency single for downstairs. The cost of the dual vs triple is substantial. I bought the 16 seer dual for upstairs and a 25 seer unit for downstairs at very nearly the same price as a triple

The ceiling cassettes do typically come with a built-in condensate pump. You'll want to buy an auxiliary one from my experience. Poor lift performance, and added reliability.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
What I've done on those is to run my main drain line to the cassette and then make an indirect connection to it, so the pump is lifting only the 12-18" to the indirect drain. I avoid anything that needs pumping as best I can.
 

monkeyspanners

Well-known member
Joined
May 28, 2013
Messages
419
Location
Oxford, UK
There is usually about a 600mm lift on a cassette for the condensate water. You don't need to use all the 600mm if its not needed for the fall, the drain needs to fall 1:100 so you can run it nearly 6m without an external pump.
 