Standby Generator What is the install cost
Jazzman442
Tampa Bay area, FL
I am getting ready to purchase a standby generator for my house. I am getting quotes for the install from the electrical company's and my gas company.
What should be the cost for each?
20KW running Propane and a automatic switch.
kd3pc
Northern Neck
you might get a quote from an independent electrical contractor...sometimes the utilities are cheaper some times not.
Not enough detail to give you much, as the install depends on distances to and from the unit, and to the electrical panel, and how accessible that path is. Whether there is space available and so on.
depending on the cost of the actual generator and the features you want (auto start, auto test, maintenance, etc) the cost of install could vary.
Falcon67
Merkel, TX
thammel
Maryland
I installed a Winco 8kw. I did all the electric myself. Only thing I paid someone to do was the propane connection. I think that was $250. The generator and ASCO automatic switch cost about $3500. This is plenty big to do everything except AC or heat pump.
Tom
mm08822
You really need to provide some details. Without anything further, this is no better than asking what a car costs!
How much in house is gas powered vs electric?
Let’s start with some basic q’s:
  • What do you want to power?
  • Must have loads,
  • Nice to have loads?
Details of ac load(s)
Sq ft of house
Location of gen….. ground level or up on a raised platform? If platform...how high?
If ground level – what type of base – pea gravel, pre-cast pad, poured pad, etc?
Access to gen location
Wiring distance to main panel from gen
Distance from gen to to gas supply, do the existing lines need to be increased?
Pics of gen location, main panel (cover open), gas supply, etc.............more is better.
Wifi connectivity to gen? etc?
What portion of the install are you willing to do?
Some 22kw units consume less fuel than 20 KW’s
Condition of main panel
Is this an opportunity to upgrade main panel due to current loading, deteriorated condition, etc?
J
Jazzman442
Tampa Bay area, FL
I am getting the 20KW from Costco. They have then on sale with the automatic switch. The unit will need 40 feet of cable to get to the Circuit breaker panel. My house is all Propane and I have a 500 gallon tank all I will need is a hook up to the Generator. It will need about 50' of the Yellow bury pipe they use here in Florida. What should the install cost be for this.
Since my house is all gas I have a 200 Amp panel and a few spaces left. One electrical contractor came today that is why I know what I said above.
You are right on the 22 KW costing les to run but the Price on the 20KW with 7 year warranty is just to good to pass up.
What has it cost others to install one of these.
Thank you
mm08822
Thank you
So if you want any credible guestimate on cost you will need to answer each q posed to you. If you dont, then there will continue to be cloud shoveling back and forth.
matt_i
It wouldn't surprise me to be (gen cost) * 2 for the turnkey install.
I was looking a few years back and that's the feeling I got at the time.
mm08822
My sell price is $10.5 - 11K (gas, electric, gen, poured concrete base) without knowing any other details. Permits excluded. Your local rates may vary.
yeldogt
Mine required load shedding -- a fully automatic generator needs to be able to handle any and all loads. Stoves/Ovens/Dryers and AC units need to be factored -- the unit needs to be large enough or smart enough (load shedding) to take care of everything.
My inspector wanted to see it spelled out
Thank you
Since you will have an ATS, can the generator handle the entire connected load WITHOUT load shedding management?
yeldogt
That is the key question, but most ATS now a days do have load shedding built in. Lots of wiring to get it all working !
Mine will do four loads -- using two load shedding panels. Each panel has 2x 50amp relays. If they are in the same location 5 wires from the unit will do. They share a common. If you want a separate control panel and all the goodies -- it takes 11 low volt wires to the house from the unit.
Platonic Solid
CT-USA
My setup sounds the same as Jazzman442. No mention of load shedding management when mine was installed. It's connected directly to my main panel. Haven't had any issues for the past 6+ years.
Its required by electrical code and has been for awhile.
Sounds like whoever installed yours didnt know code.
mm08822
A load calculation is required for any generator with automatic xfer capability. An electrical load calculation is required as part of permit submittal if the Inspection office knows what they are doing. The generator must be capable to carry the full documented connected load unless appropriate (documented) load shedding of select items is provided.
Likewise, a gas riser diagram with loads, pipe sizes and distances is needed for the fuel delivery system.
This is why I asked the OP for house sq ft, gas loads vs electric load, and the most typical common item affecting gen size - ac load(s) data. With this info it is easy to tell if gen is properly sized and if load shedding of some/all large loads required. This also affects purchased hardware and labor cost! (The original question posed by the OP.)
Since the Op chose to only answer some of the requested info, he only gets a partial answer that can be mis-leading.:dunno:
Platonic Solid
CT-USA
I'm not an electrician and make no claims of knowing code. My install was done by a licensed electrician and it was inspected. If I read mm08822's post correctly, maybe load shedding isn't required for my install due to generator being capable of handling full documented connected load.
mm08822
That could be the correct scenario. The question is, did your sparky document and submit that info or was it not needed by your AHJ? I know all don't require it, and therefor have no way of knowing if that code requirement is met. (Might not even be aware of it.)
If not, I would be inclined to say no worries after 6 years of running!
Properly applied, load shedding is a method to enable the purchase a smaller, lower cost gen and ascertain no overloads/brownouts occur within the home during use.
yeldogt
Electric Ranges/Dryers and AC/ HP are the problems. Most dryers will not restart .. but the system needs to be able to deal with the load if someone forgets and turns it back on. 20kw will run a lot of stuff -- but, it adds up quick if all electric.
Want2race
I had 3 companies bid a 22kw system
Prices were $8k to $11k all in. So given relations pricing it is $5k in labor /profit
Mine was complex. 80ft gas line but otherwise simple.
Chris_the_wrench
Chinook Pass
I put a Cummins 20kw in last summer. I paid about $5000 for the generator and auto switch. I poured the concrete, dug all the trenches and placed the tanks probably $800'ish. I hired out the electric work. My system required swapping out the meter because the way my house and shop were initially wired up. Electrician labor, parts and permits were about $2200. So around 8 grand total for my install. The winter before the install we lost power dozens of times, this winter once. But that one time I was sitting in my hot tub with music while my 'neighbors' were looking for candles/flashlights.
-Chris
jade97
38kW General installed $18.5k, not including the 500 gall propane tank, $2500 ATS or concrete pad installed when the house was built.
J
Jazzman442
Tampa Bay area, FL
I have all of these4 things answered already. My house uses propane for everything except my pool ( not worried about that in a power outage) but it has a variable speed pump. I will just need a 20KW backup
J
Jazzman442
Tampa Bay area, FL
I am not sure why this matters but here it goes.
Entire house Propane.
2 Ac units brand new Strait AC. 4 ton and a 3.5 ton.
3200FT living ac.
Tv's Lights is all I need.
Pool Is a variable speed pump and a strait 2 HP pump. Neither need to run when power is odd.
Platonic Solid
CT-USA
Looks like I paid $931 (Nov.2011) for propane tank to generator hookup (buried line from tank to gen) and $1110 for transfer switch hookup. Not sure why my meter had to be replaced, but that charge was combined with the old service riser replacement @ $1050.
yeldogt
3200FT living ac.
Jazzman: Not many years ago there were not as many choices in the home generator market (air cooled). The units being 8-12kw, most people added a sub panel with dedicated necessary items -- this sub panel became the limiting factor for the generator --- as the whole house was not connected. Today, with more affordable choices and larger air cooled generators available, people want to run more items and also to have the whole house switch over ... that does not = the generator being able to power everything should it all be on when the main service goes out.
In many parts of the country with inspections -- the rule is you must provide the potential load and the generator must be able to provide this power or have a way to keep items from coming on.
In my case the largest air cooled Cummins is 20kw -- it can't run everything in the house .. at once. With AC -- it's the start up amps 2x running amps. So while the unit can run them -- it can't start them together.
This is why you will see the unit have "load shedding" -- they monitor the load and bring the additional loads on in a cycle .. and drop them the same way.
With a manual transfer switch -- the owner has to be there .. so the theory is they are managing the load.
mm08822
Great information. I already have my entire hows plumbd for propane. Everything that can be powered by it is.
On my install all they have to do is connect it to the power box and connect the propane hose.
Your whole house xfer switch will go in between meter and panel. May require a little more work than just slapping on the wall – depends upon available space. The cable from xfer switch to panel needs to be 4 wire or equivalent. Grounds needs to be removed from neutral bar and placed onto new ground bar. (Your main panel in now a sub-panel.) GEC’s need to move from the old main panel to the xfer switch or need to be replaced/lengthened. You might need a couple of new grd rods depending on when house built.
Propane connection into the existing system needs to be made at the correct location so the gen receives proper flow and pressure and does not starve other loads along the way. This is the purpose of the gas riser diagram/calculations.
Even knowing distance isn’t the full story. Is it underground, inside, under patio, sidewalk, through the garden beds…………….
A lot more than 4 q's...........
3200FT living ac.
These details matter because it is required information used in the load calculations for the connected loads and determining if load shedding is needed/ generator big enough.
SQ FT of house required b/c general lighting load is accessed @ 3va/sqft. So yours is 9600 va >> 9600w.
Add 2 small applicance ckts @1500va >>3000w
Add 1 laundry ckt @1500va >>1500w
Pool Pump 2 hp>>>2750w
First 10kw of above is assessed at 100% in the calculation. = 10KW
Over that @ 40% = ~2800w
Plus
4 Ton Ac (need the n/p min ampacity) Assume 20 amps @240v = 4800w
3.5 Ton Ac (need the n/p min ampacity) Assume 17.5 amps @240v = 4200w
Total ~ 21,800w (there are obvious omissions in the above listed loads) >>>>> So you need load shedding capability hooked up if using a 20KW gen. Also want some headroom on the gen to handle A/C constant cycling. Load shedding on 1 a/c unit is best but you could apply it to the pool pump and technically be under 20KW.
Load shedding needs to be interconnected to the chosen device(s). Depending upon interface required it can require more hardware, certainly cable of some type and extra labor.
You didn’t answer about gen pad requirements, gen location access………a pea gravel box with pre-cast pad costs less than a 4’ high platform, or a 6” poured in place pad, etc.
Now these q’s should have meaning. Cost is based upon scope of work and degree of difficulty in doing each step. That is the msg I am trying to convey and w/o pics who knows unless 1000 q's are asked.
What should be the cost of Wiring? And Cost for connecting to propane?
See above points. Only you know the site conditions and the ease or difficulty of your job. Only PlatonicSolids reply has the necessary info via pics to convey any relative degree of cost.
Jazzman: Not many years ago there were not as many choices in the home generator market (air cooled). The units being 8-12kw, most people added a sub panel with dedicated necessary items -- this sub panel became the limiting factor for the generator --- as the whole house what not connected. Today, with more affordable choices and larger air cooled generators available, people want to run more items and also to have the whole house switch over ... that does not = the generator being able to power everything should it all be on when the main service goes out.
That's exactly the situation. (I however question the reality of manual load management!)
yeldogt
mm08822: The manual situation is interesting ... assume there is no way to control for the potential overload should a homeowner try and run too much. I'm sure the whole house have some way of protecting themselves -- it seems the load calculation are as much to protect the homeowner from a bad install as much as anything.
highflier
Navasota, Texas
Fwiw, skipping the sizing calculations....
I’m having a 20kw Briggs installed 60’ from my meter base and running on LP.
No cost yet on the LP connection but my supplier stated it should be about $250.
I have a variable speed AC that’s locked amp draw is only 10.8, in my case I will not need load shedding.
As to the quotes I got, none included LP connection and all were on poured concrete base.
Company 1 - Generac 20kw - $11,000 installed with 10 year warranty
Company 2 - Generac 22kw - $14,000 installed with 10 year warranty, was told initially I needed a 38kw and his first shot was $20,000. After helping him check the proper boxes on his iPad, 22kw @$14k. He also shared that I was paying $1300 for the ‘free warranty upgrade’ and I could drop my price accordingly if I skipped the extended warranty.
Company 3 - Briggs 20kw - $8,900 installed with 7 year warranty.
I’m going with Company 3.
All the gensets cost close to the same, $4100-4500 so you can see the math what the install charges are.
I considered other portable setups, big welders, etc. but I travel a bit and need it to turn on by itself for the family when I’m not home.
truckman5000
Just get acouple quotes.
Im a plumber, and my electrician does the electrical work for these for 1000-2500. The 2500 would be the hardest install.
Gas..580-1500. Depending on underground/ inspections.
GAs 10ft from a meter/ regulator. $580 +permit.
Electric, if you do a full transfer switch / mounted out side/ generator close. $1000 electric.
Fixin'Stuff
HotterNHellHouston
Be sure to keep your propane tank filled during hurricane season. Running that beast 24 hours a day will **** down a startling amount of propane. Also keep in mind that propane tanks can only be filled to 80% of rated capacity, so your 500 gallon tank really has only 400 gallons when "full". Use the 400 gallon number to calculate your run times.