Sub panel question

TireChanger

Member
Joined
Jul 26, 2015
Messages
6
Hello I’m looking to add a sub panel to a lean to I had built and after doing lots of research I get the idea of how it all should be wired. But now I look at my main breaker box and the neutral bar and ground bar look, full at least the ones that have a bigger screw to accept the wires from the sub panel. My question is there is a strip on top of those with smaller screws they look to be connected but I want to make sure I can tie into those with the nuetral and ground wires coming from the sub panel? One sub panel is already coming off of the main breaker box which is why the big screws are already taken.
 

Attachments

  • IMG_3719.jpeg
    IMG_3719.jpeg
    673.1 KB · Views: 46
  • IMG_3716.jpeg
    IMG_3716.jpeg
    591.2 KB · Views: 43
  • IMG_3717.jpeg
    IMG_3717.jpeg
    617.5 KB · Views: 35
  • IMG_3718.jpeg
    IMG_3718.jpeg
    639.4 KB · Views: 35
  • IMG_3720.jpeg
    IMG_3720.jpeg
    546.6 KB · Views: 33
  • IMG_3721.jpeg
    IMG_3721.jpeg
    525.9 KB · Views: 32
  • IMG_3722.jpeg
    IMG_3722.jpeg
    428.4 KB · Views: 45
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,164
Location
NJ
Easiest would be to add a bigger neutral bar.

Better yet, replace that main panel. If you don't, it is then maxed out after the latest addition.
 
OP
T

TireChanger

Member
Joined
Jul 26, 2015
Messages
6
Easiest would be to add a bigger neutral bar.

Better yet, replace that main panel. If you don't, it is then maxed out after the latest addition.
This should be the last edition haha. Could I just add the ground and neutrals that will go to sub panel to the screws above? They look rusty
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,145
Location
Modesto, CA
That is a 2 tier neutral bar.

Odd you have a bryant main with siemens branch breakers

Is there a label on the cover? What brand is the panel?

If its a bryant panel those siemens breakers need to be replaced
 
Last edited:
OP
T

TireChanger

Member
Joined
Jul 26, 2015
Messages
6
That is a 2 tier neutral bar.

Odd you have a bryant main with siemens branch breakers

Is there a label on the cover? What brand is the panel?

If its a bryant panel those siemens breakers need to be replaced

But you have no room for a double pole breaker for the new subpanel so i recommend replacement as well
Hello I saw no labels on panel. All of that was there before my time except the 100 amp breaker for the sub panel which was ran by an electrician for us. He uses a Murray box with seimen breakers is that ok?
 
To avoid these ads, REGISTER NOW!
OP
T

TireChanger

Member
Joined
Jul 26, 2015
Messages
6
That is a 2 tier neutral bar.

Odd you have a bryant main with siemens branch breakers

Is there a label on the cover? What brand is the panel?

If its a bryant panel those siemens breakers need to be replaced

But you have no room for a double pole breaker for the new subpanel so i recommend replacement as well
To make it easy I should get an Eaton sub panel and use Eaton breakers in sub panel and Eaton 100 amp breaker in main breaker box? I was reading Bryant and Eaton are compatible(same company) is that correct?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,145
Location
Modesto, CA
Hello I saw no labels on panel. All of that was there before my time except the 100 amp breaker for the sub panel which was ran by an electrician for us. He uses a Murray box with seimens breakers is that ok?
if this is a siemens panel then the bryant main should not be in there

murray was discontinued by siemens so that is fine.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,775
To make it easy I should get an Eaton sub panel and use Eaton breakers in sub panel and Eaton 100 amp breaker in main breaker box? I was reading Bryant and Eaton are compatible(same company) is that correct?
It was Bryant BR originally, then it became Westinghouse BR (Bryant was a division of Westinghouse), then Eaton bought the the electrical div. of Westinghouse, & became Cutler-Hammer BR, it's now Eaton BR.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,145
Location
Modesto, CA
To make it easy I should get an Eaton sub panel and use Eaton breakers in sub panel and Eaton 100 amp breaker in main breaker box? I was reading Bryant and Eaton are compatible(same company) is that correct?
not if your main panel is a siemens. you have all siemens branch breakers and a bryant main. so you need to figure out what brand the panel is.
 