This is my first post on GJ. I've read with interest many other threads and there seems to be no shortage of electrical knowledge (and opinions
).
I'm building out the inside of a commercial space that's about 25x50. It's just one space in a very large (100x250) building. The primary function of the space will be as a wood working shop.
I've got a 125a sub-panel mounted (with main breaker), and all the circuits that flow from the panel are either in conduit or BX.
The common / ground bus bars are not cross-connected. I will bond the ground bus bar to the sub-panel housing.
It's just me in the space, and most of my big machines are 220v. My former spot just had a 60a service, and I never had trouble with tripped circuits.
The question I have is that I don't have a 125a feed for the panel from the main power source for the building. There are 2 60a fused disconnects that are vacant. They used to feed 2 A/C compressors that are no longer used, and conveniently, they terminate outside the wall adjacent to my sub-panel. All I'll have to do is replace the disconnect boxes that are unused with 2 outdoor rated junction boxes, and add a few feet of conduit and a pull-ell to reach my space.
Unfortunately, from what I could tell, they're not wired properly, as there's no common wire at all, just 2 6ga hots.
So - here are my problems:
1) I'm going to need a common and ground wire to feed my sub-panel. I'm assuming (I've not checked), that I can find connections for this in the gutter that sits below these 2 disconnects and feeds them. If not, there should be some source for common/ground in the main panel where the service comes in.
If I have to, I'll pull the wires out of the conduits in order to add the common/ground, as I'm not certain I'll be able to add them with the other 2 cables already there. The raceways are inside the building, and are 1" EMT with 5 90-degree bends from the back of the box to the disconnects for the former A/C units (which as I understand is more bends than should be allowed...).
Or is there another way?
2) Is it OK to feed the 125a main breaker in the sub-panel with a 60a feed, or do I need to replace the main breaker with a 60a unit (if that's even possible)?
My plan is to use the 2nd 60a feed for a future A/C unit, so I'll just run the conduit from the old outside disconnect to a spot inside my space where the air handler would sit and end the wires there, properly capped.
Sorry - long post - to summarize:
2 questions -
1) Is it possible to add 1 6ga and 1 10ga (I assume that's sufficient for the ground) to a 1" conduit that has 5 bends and already contains 2 6ga conductors - without pulling the existing wires out first?
2) Is it permissible to feed a 125a sub-panel with a 60a circuit?
Thanks for taking the time to read and answer.
Regards
I'm building out the inside of a commercial space that's about 25x50. It's just one space in a very large (100x250) building. The primary function of the space will be as a wood working shop.
I've got a 125a sub-panel mounted (with main breaker), and all the circuits that flow from the panel are either in conduit or BX.
The common / ground bus bars are not cross-connected. I will bond the ground bus bar to the sub-panel housing.
It's just me in the space, and most of my big machines are 220v. My former spot just had a 60a service, and I never had trouble with tripped circuits.
The question I have is that I don't have a 125a feed for the panel from the main power source for the building. There are 2 60a fused disconnects that are vacant. They used to feed 2 A/C compressors that are no longer used, and conveniently, they terminate outside the wall adjacent to my sub-panel. All I'll have to do is replace the disconnect boxes that are unused with 2 outdoor rated junction boxes, and add a few feet of conduit and a pull-ell to reach my space.
Unfortunately, from what I could tell, they're not wired properly, as there's no common wire at all, just 2 6ga hots.
So - here are my problems:
1) I'm going to need a common and ground wire to feed my sub-panel. I'm assuming (I've not checked), that I can find connections for this in the gutter that sits below these 2 disconnects and feeds them. If not, there should be some source for common/ground in the main panel where the service comes in.
If I have to, I'll pull the wires out of the conduits in order to add the common/ground, as I'm not certain I'll be able to add them with the other 2 cables already there. The raceways are inside the building, and are 1" EMT with 5 90-degree bends from the back of the box to the disconnects for the former A/C units (which as I understand is more bends than should be allowed...).
Or is there another way?
2) Is it OK to feed the 125a main breaker in the sub-panel with a 60a feed, or do I need to replace the main breaker with a 60a unit (if that's even possible)?
My plan is to use the 2nd 60a feed for a future A/C unit, so I'll just run the conduit from the old outside disconnect to a spot inside my space where the air handler would sit and end the wires there, properly capped.
Sorry - long post - to summarize:
2 questions -
1) Is it possible to add 1 6ga and 1 10ga (I assume that's sufficient for the ground) to a 1" conduit that has 5 bends and already contains 2 6ga conductors - without pulling the existing wires out first?
2) Is it permissible to feed a 125a sub-panel with a 60a circuit?
Thanks for taking the time to read and answer.
Regards