Subpanel and conduit size question

Eric29

Well-known member
Joined
Apr 18, 2008
Messages
499
Location
Western NY
I'm placing a sub panel about 3' from my main panel. Following the good advice I received in this forum, I've decided to install a sub panel that is able to handle a 200 amp load in case I decide to upgrade the 100 amp main panel in the future.

I want 60 amps to go to the sub panel. I believe that I need three 6 gauge copper wires and one 10 gauge wire for the neutral. That could be carried in 3/4" metal conduit.

In anticipation of someday making the sub panel the main and running 100 amps back to it, I believe that I need to install 1" metal conduit to carry the copper 3-3-3-8 back to it in the future.

Am I on the right track? Should I use larger conduit for the future switch over?

Thanks.
 
To avoid these ads, REGISTER NOW!

Lonnies Performance

Well-known member
Joined
Aug 20, 2017
Messages
267
Location
Pittsburgh, PA
1" is at max capacity with the 3-3-3-8, but meets the 40% fill requirement. You can go up to 1-1/4" for a minimal cost increase if you desire. I just ran 1" for a 100A sub panel about 70'ft away.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,540
Location
Minneapolis
If it's only three feet away from the other panel, you may as well use the biggest piece of conduit that will fit - any additional cost will be pretty minimal.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,281
Location
Modesto, CA
You should make sure the subpanel is rated for use as service equipment if you plan on making it a main service panel some day.
 
Last edited:
To avoid these ads, REGISTER NOW!

whisperinsam33

Well-known member
Joined
Jun 24, 2013
Messages
124
Plus 1 for Stuart. Biggest is Bestest especially with only a 3 foot run as a cost factor.
 