Testing Compressor Contactor?

mkbug

Active member
Joined
Apr 21, 2007
Messages
42
Location
Vacaville, CA
My home's AC unit stopped. I check the breakers and two fuses and have power to the unit. I took a volt meter to the black box and have power going in to this unit, but when its supposed to be on...there is no power coming out. Can I assume that is the correct test and this compressor contactor is bad?

We are in a heat wave this weekend in California - wife wants me to call a guy. But I think with The Garage Journal's help I got this...
 

Attachments

  • IMG_0971.jpg
    IMG_0971.jpg
    96.5 KB · Views: 41
To avoid these ads, REGISTER NOW!

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
See attached pic.
Use your meter to check if you have 24V on the terminals with green arrow.
If yes, you have 24VAC and still no 240VAC output, contactor is bad.
 

Attachments

  • Screenshot_20200906-064715.jpg
    Screenshot_20200906-064715.jpg
    20.9 KB · Views: 23

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,306
Location
Coronado, CA
A compressor contactor is no more complicated than any automotive relay, just bigger.

If you apply the appropriate voltage to the coil it should go "Clunk" if it doesn't something is amiss.
 
OP
M

mkbug

Active member
Joined
Apr 21, 2007
Messages
42
Location
Vacaville, CA
I did some more testing...
I have voltage from the thermostat and into the circuit board. Photo 0797

But back to the contactor the black and blue wire had zero. Photo 0980

I followed the blue wire down to some connector on the copper line, and there was a button....I push it and heard a click. ahhhh Photo 0981.

But still nothing.

So I came back to my computer to do more research. Went back to the unit and viola it was working. Dont know why it all started again. But it is pushing cold air again.

What caused the button to pop? Do I still need a service call?

Thanks all.
 

Attachments

  • IMG_0981.jpg
    IMG_0981.jpg
    115.4 KB · Views: 34
  • IMG_0979.jpg
    IMG_0979.jpg
    127.9 KB · Views: 30
  • IMG_0980.jpg
    IMG_0980.jpg
    81.2 KB · Views: 27
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,372
Location
Michigan
The switch is a manual reset high pressure switch, dirty condenser coil or fan not operating is the normal reason that they will trip. Circuit board has a time delay that's why it didn't start right up.



Sent from my SM-T510 using Tapatalk
 
OP
M

mkbug

Active member
Joined
Apr 21, 2007
Messages
42
Location
Vacaville, CA
Looks like the high pressure cut out switch, Is the condenser clean?
Fan on top running ok?

Fan was running but we did clean up some leaves etc. So much better now.


THANK YOU ALL THAT CONTRIBUTED.

Happy wife - happy life.

Martin
 

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
With your knowledge of how to use a volt meter , I knew you will be able to perform diagnostics.
Good job.
 