Upside down panel
kvom
*******, GA
In another thread there were some examples where the panel was installed upside down, so that when the service cable entered from below the connections would be shorter.
I asked my electrician about that, as I had that situation, and getting the cables up and over to the connecting lugs was a bit of an effort. He said that doing that was against code. Don't know if that's in GA only, but anyone considering this "option" ought to check first.
Aceman
Eastern Oregon
I'll summarize 240.81 for you.
"Where circuit breaker handles are operated vertically, the up position will be on." All breakers should clearly indicate when they are on or off.
So, if you meet that code secton above and your panel's instructions allow you to flip the guts, you're alright. But it's always a good idea to check with your inspector in case you have some wacky amendment to the code that doesn't allow it.
trainer
Northern Ontario, Canada
Mine's installed updside down. The service mast and meter are directly outside the panel. The meter and main breaker line up directly, making for a really clean installation, and keeping the panel at the required height off the floor.
My dad had one in his cottage mounted sideways. It was the only way to get a 40 circuit, 200a panel the required distance from the floor on the short walls there.
I'm certain that the manufacturer of the equipment would need to approve it for this type of installation though
twostory
Duluth, Georgia
I live in Gwinnett Co, Georgia. I asked my inpsector before I did any work if I could install the panel upside down. He said no, so my panel is right side up with the big wires doing a big 180 turn at the top of the box, since they enter at the bottom of the box.
Torque1st
MEMBER EMERITUS
KC Metro, Kansas
Most new panels are made to install main breaker on top OR at the bottom. Check the stamped in nomenclature in the enclosure and the installation instructions. Many people are used to seeing them with the main breaker at the top and figure that is the only way they should be mounted. Make the inspectors show you chapter and verse in the code.
brad d
Winnipeg
Funny I was going to ask the same question... but i just installed them right side up.. I'll just bend the wire 180* :(
Charles (in GA)
50 mi south of Atlanta
Square D breaker panelboards use horizontal main switch levers, my house panelboard has a fold out lever for ease of operating. Of course, if you use a main lug panel, you don't have the main panel breaker to be concerned about.
Charles
nadogail
Coronado, CA
My Main Panel, on the garage exterior is "Top Fed" from and Overhead Drop from the pole in the alley.
The Sub Panel in the house is "Bottom Fed" from an underground conduit.
Bert_
NW Iowa
And modern loadcenters do not have a "right side up" or "upside down" it is either top, or bottom, feed.
Exactly. There's a reason the mains all operate sideways and the labels are readable from either direction these days. There is no upside down.
jagwinn
Virden, Illinois
And...your panel should fire Right to Left...