Uses for Buss Drop Cable - Welder leads? Jumper Cables?

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
So I've got half a spool of new 600V 8/3 Buss Drop Cable, good for 40Amps. What can it be used for? Welder leads? Home made Jumper Cables? Machine cords? It is a flexible and rugged cable meant to be abused. It has 3 wires. Can I use for single phase?
 
To avoid these ads, REGISTER NOW!

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
Bout the only use I see is heavy duty extension cords, 120v, or 240V on equipment where neutral is not needed, or line cords for machines.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Would make a wonderful 1Ø welder extension cord, as long as one does not stick a 4sq (1900 box), or a 4 11/16 sq box on the end, bad news when that is done.....
 

ElectroLight

Well-known member
Joined
Jan 5, 2011
Messages
494
Location
Rockville, MD
You could make a real nice extension cord for 240V welder. 8Ga is nice stuff but the fact that it's 3 conductor is what limits your creativity with it. How many feet of it do you have?
 
To avoid these ads, REGISTER NOW!

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,045
Location
NJ
So I've got half a spool of new 600V 8/3 Buss Drop Cable, good for 40Amps. What can it be used for? Welder leads? Home made Jumper Cables? Machine cords? It is a flexible and rugged cable meant to be abused. It has 3 wires. Can I use for single phase?

Welder leads? Nope, really not enough ampacity there for 'most' welding. #8 AWG copper is not 'big' enough for most welding, except maybe some low-amp stuff (remember, the 'rated' ampacity there is just 40 amps, and that's on 120 or 240 V with the heating and voltage-drop allowable on those voltages, welding is running much-much lower arc voltages so the % voltage drop comparge to 120V or 240V powerline voltages is much greater.)

Most of the welders I know of or have looked at/up have leads that start at #4 AWG copper, btw. And those are the low-amp low duty-cycle ones with 'short' leads.

Same rationale for using it as jumper cables, Nope. Too much voltage drop % on the lower DC voltage for 12V or 24V high-amp (jumper cable) usage.

Unless you have a need for the buss drop cable, I'd probably suggest to sell or trade it and get what you want or need. Anything else (besides a buss drop :D ) is using it in a semi (or completely) makeshift manner.

http://www.southwire.com/products/BusDropCable.htm

http://www.southwire.com/products/blackNonULWeldingCable.htm

YMMV.

re: number of phases The wire really doesn't 'care' about the number of phases being conducted as long as the number and size of the conductors and the insulation are 'proper' for the task at hand.
 

jam0o0

Well-known member
Joined
Jul 14, 2009
Messages
244
Location
Katy, TX
8 gauge will work great for jumper cables. just need some ends.

if you have 3 prong welders then the 3 wire cord will make a great extension ( between machine and wall). hell my miller 180 only pulls 22 amps.

disclaimer: i'm no electrician.
 