wall heater wire size

BADSIX

Well-known member
Joined
Nov 30, 2010
Messages
895
Location
oregon coast
I have two bedrooms and i'm going to put 1 heater in each room .they are 6.25 amp and 1500 watts. they will be wired to a single double pole 20amp breaker with # 12 wire. from the breaker to a junction box then to each heater . does this sound correct, will the single no. 12 wire from the breaker to the junction box be big enough to handle the two heaters.
Jay D.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
#12 wire is capable of handling two 1500w heaters at 240v.

You need a thermostat within sight of each heater that opens both "hot" wires and has a marked "off" position OR you need to install a breaker lockout at the panel on the circuit breaker feeding these heaters.
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,310
Location
Niagara Region, Ontario, Canada
------------------
You need a thermostat within sight of each heater that opens both "hot" wires and has a marked "off" position OR you need to install a breaker lockout at the panel on the circuit breaker feeding these heaters.

not heard of that . infact an apt. building I work in is upgrading the panels , moving the location of panel to be code compliant , installing gfi breakers for kitchen and no lockouts for electric heat. I think if that was code they would do that too.
 
To avoid these ads, REGISTER NOW!

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
If the heater doesn't have an internal breaker or off switch that disconnects both legs and some other rules.

424.20 Thermostatically Controlled Switching Devices.
(A) Serving as Both Controllers and Disconnecting
Means.
Thermostatically controlled switching devices and
combination thermostats and manually controlled switches
shall be permitted to serve as both controllers and disconnecting
means, provided they meet all of the following
conditions:
(1) Provided with a marked "off" position
(2) Directly open all ungrounded conductors when manually
placed in the "off" position
(3) Designed so that the circuit cannot be energized automatically
after the device has been manually placed in the "off" position
(4) Located as specified in 424.19
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
not heard of that . infact an apt. building I work in is upgrading the panels , moving the location of panel to be code compliant , installing gfi breakers for kitchen and no lockouts for electric heat. I think if that was code they would do that too.

I don't use other electricians work as a baseline for what our shop does.

I follow the code book.

Stuff has posted the code rule. Your apartment electricians might need to have that pointed out to them. In my experience when they miss one thing....there are others as well.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
not heard of that . infact an apt. building I work in is upgrading the panels , moving the location of panel to be code compliant , installing gfi breakers for kitchen and no lockouts for electric heat. I think if that was code they would do that too.

What others have done is not always a example to be followed Aceman & Stuff, have given pretty good reasons why.
 