I am wiring my shop and want to put in a circuit in case I ever want to pug in a welder.
1. I have enough 8/2 w/ground and a 40 amp breaker on hand.
2. I have a small shop (14x24) and will never do heavy duty fabrication work there.
3. If I buy a welder, it will most likely be a fairly small MIG. I cannot fathom any need for a heavy welder and if I do need one, I have access to a couple nearby.
4. The path to upgrade later is not a huge deal. It would involve removing an access panel and running some conduit on the outside of the wall (under my workbench). It isn't what I want, but it could be done.
Shall I put in the 40 amp circuit and be done with it? Or spend the $120+ it will cost to put in a 50 amp circuit?
John in OH
SE Ohio & Eastern Virginia
If you look at the specs for a typical small MIG welder, such as a Hobart Handler 187, you will find that the input to the primary side of the machine is 20.5 amps at 240volts at rated load. So you should be fine with a 40 amp feed.
On a historical note ... back in the 1950s-60s, the Rural Electrical Authority (REA) that served rural areas of America, established a maximum single point load limit of 40 amps for any given load at a farm. At this time, stick welders were growing in great popularity in the US so to address this 40 amp limit, most welder manufacturers designed and sold a simple transformer-type welder (buzz box) that required a maximum input of only 39 amps. These machines gave a maximum secondary (welding current) output of 180 amps. At 180 amps you can do some serious stick welding!
So, even if you choose to go with a stick machine you could still use the 40 amp circuit ... assuming you could find a used 180 amp welder on eBay or at an auction somewhere. As far as I know, this old REA limit no longer exists and I don't know of any manufacturers that still make a 180 amp machine ... but I have not researched the subject.
Strouty
Southern Maine
I have a large miller shopmaster 300 amp and it only uses a 80 amp circuit. I think you will be fine with 40.
John in OH
22rifle ... I just took another look at your original post and now note you are proposing to use 8/2 with ground cable (I assume this is a bare ground).
A cable with only 2 conductors and a bare ground will work OK if the welder is a purely 240 volt load, but if the welder you purchase also has any 120v accessories or drives you will need a cable with 3 conductors and a ground. In the old days you could use a 3 conductor cable (no separate ground) with all 3 conductors insulated, but I think that technique is now frowned upon.
I don't own a small MIG welder so I can't comment on this issue ... you need to get advice from someone on this board that has such a machine or check one out at a dealer. The issue isn't really the 40 amp capacity which is OK, but whether the cable you have has adequate number of conductors.
BBQ&Love
Texas
Was thinking about that. My welding experience is pretty limited. Other than a little repair, I have only welded extensively with 3 welders in my life. The stick Lincoln I grew up with. My FIL's MIG (whatever it was; I built a custom 16' trailer with it), and a little 120 volt Lincoln wire feed I used to own. So I don't know if the 120 leg is ever an issue or not.
sberry
Brethren, Michigan
You will be fine with the 8/2wg, its all they need. It will run a 50A stick machine and any current unit that comes with 50A factory cord.
Norcal
It is not likely that a neutral would be required, if the machine required 120V it would be derived internally in the machine.
BBQ&Love
Texas
Well today I acquired enough 6/3 with ground UF wire to do the run. Well, it's actually 3 times as much as I need.
Cost? 5 minutes and $0.00!
Solved that problem.