mikeyr
Well-known member
I am trying to avoid a argument with the company I purchased a jacuzzi from, they installed it today and I think they wired it wrong.
The manual clearly states 6g wire and 50amp breaker, I got home and they ran 8g and 40amp breaker. Says that is all they ever do and its fine, I have to admit they have been in business since the 1970s and its the second spa I have bought from them so I tend to trust them.
So they have offered to come and put in a 50amp breaker tomorrow but of course not change the wire, they claim it will be ok with 8g wire since it is only a run of about 40ft. I am guessing 40ft. the spa is actually about 30ft. from the panel so adding some for going down under the house, etc. He says for that short a run, I will have no problems.
If I do the math on both pumps, they draw 16.5amps total, the heater I don't have specs for but he says its 20amps (have to trust him) and the light is LED so no draw of consequence. That puts me at 36 amps and I have run everything on without popping the breaker.
I would prefer avoid a war with them and either leave the 40amp breaker in there since it is working AND they claim that is all they ever put in for that spa and no issues. Do I need to make a war to upgrade the wiring ? can I go to 50amp breaker since its such a short distance as he says.
And by the way, permit was signed off by city inspector so he thinks its ok at 40 also but I think he just looked at how things were done nothing else.
The manual clearly states 6g wire and 50amp breaker, I got home and they ran 8g and 40amp breaker. Says that is all they ever do and its fine, I have to admit they have been in business since the 1970s and its the second spa I have bought from them so I tend to trust them.
So they have offered to come and put in a 50amp breaker tomorrow but of course not change the wire, they claim it will be ok with 8g wire since it is only a run of about 40ft. I am guessing 40ft. the spa is actually about 30ft. from the panel so adding some for going down under the house, etc. He says for that short a run, I will have no problems.
If I do the math on both pumps, they draw 16.5amps total, the heater I don't have specs for but he says its 20amps (have to trust him) and the light is LED so no draw of consequence. That puts me at 36 amps and I have run everything on without popping the breaker.
I would prefer avoid a war with them and either leave the 40amp breaker in there since it is working AND they claim that is all they ever put in for that spa and no issues. Do I need to make a war to upgrade the wiring ? can I go to 50amp breaker since its such a short distance as he says.
And by the way, permit was signed off by city inspector so he thinks its ok at 40 also but I think he just looked at how things were done nothing else.