I've seen it hundreds of times. It doesn't trip until someone (me) pulls the receptacle out live, it then falls apart and usually the hot shorts to the neutral, sometimes the ground.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I have seen several of these from long term heavy loads, but I have also seen old breakers fail to trip even under a fault
 
To avoid these ads, REGISTER NOW!

ybnormal

Well-known member
Joined
Jan 3, 2016
Messages
5,002
what's loose tangs got do with it?

our house got hit by lightning, came down inside thru the spinning roof ventilator, hit the cable line running thru the attic which was plugged into a booster wall-wart plugged into a bedroom wall, did the same thing as pictured above and blew it off the wall. the lightning then backfed thru the whole cable out to the demarc, from the demarc to the mother-in-law apartment out back, and then the opposite direction from the demarc across and underneath the street to the feed box. took out the whole line, Spectrum had to come out and run a completely new line.
 

Mainiac Mat

Well-known member
Joined
Sep 2, 2020
Messages
409
Location
Maine
I believe breakers are primarily protecting the circuit wiring (hence their full name is circuit breaker). Specifically, they limit the current to prevent the insulation from breaking down. Faulty connections at an outlet can generate heat and sparks and not exceed the trip rating of the breaker.

If there was an arc with the attached plug, I think an arc fault breaker would have tripped, as they have a little computer in them and measure both the outgoing and return current. If there is a mismatch between the goes in and comes back (due to arcing in an attached device), the breaker will trip.

But if a loose connection increased resistance and I2R losses generated heat untill the plastic melted, then no breaker would trip, until the melting caused a short circuit.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,368
Location
Coastal NJ
I think an arc fault breaker would have tripped, as they have a little computer in them and measure both the outgoing and return current. If there is a mismatch between the goes in and comes back (due to arcing in an attached device), the breaker will trip.
That is the description of a Ground Fault Circuit Interrupter. Not an AFCI.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
Bad connection causing high impedance. I2R looses did the rest.
Same effect with this igbt. Until it quit.
36E2B604-5FF5-40B9-9640-203A6F658700.jpeg
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,244
Location
Modesto, CA
I believe breakers are primarily protecting the circuit wiring (hence their full name is circuit breaker). Specifically, they limit the current to prevent the insulation from breaking down. Faulty connections at an outlet can generate heat and sparks and not exceed the trip rating of the breaker.

If there was an arc with the attached plug, I think an arc fault breaker would have tripped, as they have a little computer in them and measure both the outgoing and return current. If there is a mismatch between the goes in and comes back (due to arcing in an attached device), the breaker will trip.

But if a loose connection increased resistance and I2R losses generated heat untill the plastic melted, then no breaker would trip, until the melting caused a short circuit.
No that is what a GFCI does not an AFCI
 