What about stranded THHN. (3) 4 gauge for conductors and neutral with a 6 gauge ground?
What size conduit? 1.25”?
What size conduit? 1.25”?
1.25 will accomodate easily that combination. You can still run a reduced neutral. The conductors need to be #4 copper good for 85A. OCP could be 90A if calculated load no more than 85A.What about stranded THHN. (3) 4 gauge for conductors and neutral with a 6 gauge ground?
What size conduit? 1.25”?
I pulled thru 1.5" until I hit a 90, then I had to cut it out. 2" works fine, even solo.It pulls fine through 2" or larger. Run a pull string first, use cable lube. 2 man job, one pushing, one pulling... a 40' run I could probably do myself.
Conduit is supposed to be completely installed & then pull the wire, and when bending PVC, a cool wet rag will set it quickly, it's not a code recognized method but a weed burner works pretty good for larger conduit, as does a heat gun.If you want an easier pull go with long sweep bends. It makes a lot of difference. I had trouble getting any long bends less that 2" locally so just ran some steam from a kettle through a larger pipe for a few minutes with the PVC inside and it was easy to bend. Layed it on the floor that was tiled so I had some idea of dimensions and held it for a few minutes until it cooled.
I found it much easier and got a much more even bend with the steam than my heat gun (which was a fairly small one but went to high temps). Found it hard to get much length hot enough to bend in anything over about 1" diameter so ended up with a bunch of points of sharper bends and a lot more messing with it for a 24" radius.Conduit is supposed to be completely installed & then pull the wire, and when bending PVC, a cool wet rag will set it quickly, it's not a code recognized method but a weed burner works pretty good for larger conduit, as does a heat gun.
Steam works to soften PVC my comment was mostly that the conduit goes in 1st, then pull wire.I found it much easier and got a much more even bend with the steam than my heat gun (which was a fairly small one but went to high temps). Found it hard to get much length hot enough to bend in anything over about 1" diameter so ended up with a bunch of points of sharper bends and a lot more messing with it for a 24" radius.
Yep. Don't want the heat or glue on the wires.Steam works to soften PVC my comment was mostly that the conduit goes in 1st, then pull wire.
It's the transformer for the doorbell.Does anyone know what this little gizmo is? Some kind of transformer? I am cleaning up things in the bottom of my main panel in preparation for running power out to the sub panel. Here is how this thing is connected. Neutral lands on the neutral bar. One wire from it goes to a wire nut in the bottom of the panel. It’s connected to a wire that runs to a breaker. There are two wires connected to that breaker. The breaker is labeled “general lighting”. The other wire running from this metal device comes out of the bottom of the box and runs to romex disappearing into a stud (the wire I have my finger on) . There are some old lights in different parts of landscaping that are broken, ripped out and basically non functioning. Could it somehow be related to those? If it really is serving no function I would like to take it out of the box.
Thank you.It's the transformer for the doorbell.
Calling 120 volts "high voltage" is a bit much,Odd location for a doorbell transformer. Low voltage wires in high voltage space must have insulation rating of high voltage area or have a partition to separate them. I can't see the low voltage connections but likely that requirement isn't met. The doorbell transformer usually is installed in a knockout so only the high voltage side is inside. Looks like this one has a lock ring (thin threaded nut - probably has an industry term I can't think of at the moment) so could be mounted that way. Mine is on an electric box on the side of my furnace.
I think it was pretty clear if not exactly accurate terms. If you want to get technical using "low voltage" to apply to less than 50 V isn't correct either. It's ELV - extra low voltage. And from what I quickly looked up (could be wrong) doorbell circuits are SELV - safety extra low voltage. Those are under 50 VAC and don't have a connection to earth so a single fault to earth doesn't cause any issue. So the OP connection to neutral isn't correct either. But we came to the same basic conclusion - it shouldn't be in the panel.Calling 120 volts "high voltage" is a bit much,even 480 volts is considered low voltage, I always prefer to call it low voltage & line voltage, since true high voltage has the ability to reach out and touch you if get too close. That transformer should not be inside the panel.
I just cringe when reading "high voltage" describing 120V or 240V, which is the whole reason for my comments, while it seems more common than it should, most agree the door bell ****** should not be in a panel.I think it was pretty clear if not exactly accurate terms. If you want to get technical using "low voltage" to apply to less than 50 V isn't correct either. It's ELV - extra low voltage. And from what I quickly looked up (could be wrong) doorbell circuits are SELV - safety extra low voltage. Those are under 50 VAC and don't have a connection to earth so a single fault to earth doesn't cause any issue. So the OP connection to neutral isn't correct either. But we came to the same basic conclusion - it shouldn't be in the panel.