Came home from work and saw the master bed side of the house was 77 degrees, thermostat set on 74. Cycled it off, on. Blower fan kicked on and stopped after 20 seconds. Could not hear the condenser fan running.
40a 220 breaker was tripped. Reset the breaker and it tripped in a second.
Went outside and cleaned the condenser, looked at all connections, tested the condenser fan. Black/Purple = 21.8 ohms, Black/orange = 25.0 ohms, purple/orange = 46.5 ohms
Tested the start capacitor (Surephon CBB65A 45+10 mfd +/- 5%) Com to Herm = 41.2 mfd, Com to fan = 9.69 mfd.
Both seem fine. So I unplugged the compressor and reset the breaker. Did not trip. Condenser fan kicked on, interior blower fan ran as well. Big draw on the compressor to trip breaker makes me think it is shot.
Armstrong Air 4SHP15LE142P-1
Circuit board had both red/green slow flashing = normal operation/power to control. 5 years old.
Anything else it could be?
Can the compressor be replaced or do the entire outside units get replaced? Rough price for replacement? HVAC tech will be called tomorrow so I am trying to prep myself for damage lol.





40a 220 breaker was tripped. Reset the breaker and it tripped in a second.
Went outside and cleaned the condenser, looked at all connections, tested the condenser fan. Black/Purple = 21.8 ohms, Black/orange = 25.0 ohms, purple/orange = 46.5 ohms
Tested the start capacitor (Surephon CBB65A 45+10 mfd +/- 5%) Com to Herm = 41.2 mfd, Com to fan = 9.69 mfd.
Both seem fine. So I unplugged the compressor and reset the breaker. Did not trip. Condenser fan kicked on, interior blower fan ran as well. Big draw on the compressor to trip breaker makes me think it is shot.
Armstrong Air 4SHP15LE142P-1
Circuit board had both red/green slow flashing = normal operation/power to control. 5 years old.
Anything else it could be?
Can the compressor be replaced or do the entire outside units get replaced? Rough price for replacement? HVAC tech will be called tomorrow so I am trying to prep myself for damage lol.