Hi, I have an issue with GFCI breakers being tripped for no obvious reason. I'm hoping someone has seen this before and has a solution or suggestions.
My main service comes from a transformer about 60 feet away, into a 200 Amp panel on the side of my house. I had that panel upgraded 15 years ago and there are several GFCI breakers in it, and they never trip.
I have a cable feeding a sub-panel (SP1) on the other end of the house for my AC. It's a 60 foot run of 3X 1-0 (hot/hot/neutral) and bare ground. All aluminum. Neutral is NOT bonded to ground at SP1.
For about 15 years the only load on that was a 40 Amp 240v AC unit. Note that the feed to the AC unit from that second is 2 hots and a ground (No neutral). That's worked fine for 15 years.
I added a detached garage this spring. I ran a 30 foot run of qty 4, 4 gauge stranded copper from SP1 to SP2 inside the detached garage. 2 hots, neutral, ground. 60 amp breaker in SP1 feeds SP2.
SP2 is grounded by both the ground coming from SP1 (and thus main panel in turn), as well as a UFER ground in concrete foundation at detached garage. Neutral is NOT bonded to ground at SP2.
In SP2, detached garage, I have two circuits feeding 12 or so 120V receptacles. I put qty 2, 20 amp GFCI breakers in the panel, one feeds 6 outlets the other the other 6. Breakers are new as of Jan 2023. I've triple checked that the neutrals for the LOAD are wired to the proper place on GFCI breaker, and the neutral pigtail from GFCI is bonded to the neutral bus bar.
Currently the ONLY load whatsoever is the garage door opener operating 2x per day. It is on it's own dedicated circuit in SP2. GFCI at the I've verified breaker is not tripped before or after using garage door opener. There is nothing plugged into any of the 12 receptacles on the GFCI circuits.
I am 99.99% sure it's all wired correctly with no "built in" ground faults, etc. I did the work all myself. I'm not a licensed electrician but I know to study/read/understand best practices before I jump in. I also know enough to realize I may have missed something...
The issue is, I will find one or the other of the GFCI breakers tripped every few days. One time it's on the first circuit of receptacles, next time it's on the other. Again, there is ZERO load on the 2 GFCI circuits; nothing is even plugged into any of the receptacles. After I reset the breakers, they never trip immediately. Could be one day, could be five days later.
What's odd is I also have another receptacle circuit that has a 2-pole 20 amp 120v/240v GFCI/AFCI breaker, that NEVER gets tripped. As with the others, no load whatsoever at this time.
I'm wondering if the fact that my AC unit on SP1 is running pretty much around the clock is causing some very small mismatch between the hots and neutrals inside SP2 and thus tripping the GFCI breakers in SP2.
Has anyone run into something like this?
Any suggestions?
Thanks in advance.
MAIN PANEL

SP1

SP2
My main service comes from a transformer about 60 feet away, into a 200 Amp panel on the side of my house. I had that panel upgraded 15 years ago and there are several GFCI breakers in it, and they never trip.
I have a cable feeding a sub-panel (SP1) on the other end of the house for my AC. It's a 60 foot run of 3X 1-0 (hot/hot/neutral) and bare ground. All aluminum. Neutral is NOT bonded to ground at SP1.
For about 15 years the only load on that was a 40 Amp 240v AC unit. Note that the feed to the AC unit from that second is 2 hots and a ground (No neutral). That's worked fine for 15 years.
I added a detached garage this spring. I ran a 30 foot run of qty 4, 4 gauge stranded copper from SP1 to SP2 inside the detached garage. 2 hots, neutral, ground. 60 amp breaker in SP1 feeds SP2.
SP2 is grounded by both the ground coming from SP1 (and thus main panel in turn), as well as a UFER ground in concrete foundation at detached garage. Neutral is NOT bonded to ground at SP2.
In SP2, detached garage, I have two circuits feeding 12 or so 120V receptacles. I put qty 2, 20 amp GFCI breakers in the panel, one feeds 6 outlets the other the other 6. Breakers are new as of Jan 2023. I've triple checked that the neutrals for the LOAD are wired to the proper place on GFCI breaker, and the neutral pigtail from GFCI is bonded to the neutral bus bar.
Currently the ONLY load whatsoever is the garage door opener operating 2x per day. It is on it's own dedicated circuit in SP2. GFCI at the I've verified breaker is not tripped before or after using garage door opener. There is nothing plugged into any of the 12 receptacles on the GFCI circuits.
I am 99.99% sure it's all wired correctly with no "built in" ground faults, etc. I did the work all myself. I'm not a licensed electrician but I know to study/read/understand best practices before I jump in. I also know enough to realize I may have missed something...
The issue is, I will find one or the other of the GFCI breakers tripped every few days. One time it's on the first circuit of receptacles, next time it's on the other. Again, there is ZERO load on the 2 GFCI circuits; nothing is even plugged into any of the receptacles. After I reset the breakers, they never trip immediately. Could be one day, could be five days later.
What's odd is I also have another receptacle circuit that has a 2-pole 20 amp 120v/240v GFCI/AFCI breaker, that NEVER gets tripped. As with the others, no load whatsoever at this time.
I'm wondering if the fact that my AC unit on SP1 is running pretty much around the clock is causing some very small mismatch between the hots and neutrals inside SP2 and thus tripping the GFCI breakers in SP2.
Has anyone run into something like this?
Any suggestions?
Thanks in advance.