For this 240v harbor frieght spot welder what should be the breaker size?
It's rated at 16 amps. I would use a 20 amp breaker.For this 240v harbor frieght spot welder what should be the breaker size?
And my refrigerator is in a 20A circuit.My Stick Welder is fed from a 50 Amp breaker and #8 wire.
I'd run 12/2 and breaker at 20A.For this 240v harbor frieght spot welder what should be the breaker size?
Mike in post #5 hit the nail on the head. The breaker is designed to protect the other elements of the circuit (recepticle, wiring, connectors) and to some extent, the equipment plugged in to it. If the wiring or the recepticle are not sized for 30 amps, but you use a 30 amp breaker, you risk damaging your circuit. If your device plug is not rated for 30 amps, and you use a 30 amp breaker, you risk damaging your device.Would a 30amp breaker be ok to use?
Except for hvac equipt.You will need a 20 amp circuit minimum. Breaker size is rated by the wire size, not the unit you plug into it.
From the factory there is no plug.The manual doesn't specify a required breaker size, so 30 should be fine. What plug end comes on it?
i'd expect its either a 6-20 or a 6-50 (to match most welders). You should not have a 20a receptacle on a 30a circuit breaker.
are you trying to repurpose an existing circuit?
If you don't want to.make the plug available for other welders, I'd probably put a 6-30 on it.From the factory there is no plug.
I have an existing dedicated 30amp circuit that I would like to repurpose.
I guess none of the wise electricians in this thread have an answerTangential question: what is that spot welder even good for? The only thing I know of that commonly gets serviced with spot welds is auto bodies, and you certainly wouldn’t weld on a car with those tiny little pointy electrode caps. Do people use it for light duty fabrication?

Did googling for it let you down?I guess none of the wise electricians in this thread have an answer![]()
Yes, that would be the minimum required circuit size, not a maximinum. If using a 30a, the wiring had to match that ampacity, which in nm-b, is #10. 12 nm-b with a 30 would not be okIsn't 125% of 16 = 20?
Generally, you should size a breaker for 125% of the load (or 25% extra capacity) and no less. Oversized breakers can allow wires to heat above safety levels without stopping the current. On the other hand, undersized breakers may continuously trip under normal operation.
![]()
Breaker Size Calculator
The breaker size calculator will help you obtain the correct circuit breaker size for your home panel based on the electrical load.www.omnicalculator.com
So I can plug a 30 amp heater into a 50 amp breaker and that's safe depending on "wire size".You will need a 20 amp circuit minimum. Breaker size is rated by the wire size, not the unit you plug into it.

If the wire is sized for the load and the device doesn't require the breaker for it's own protection, yes.So I can plug a 30 amp heater into a 50 amp breaker and that's safe depending on "wire size".![]()
You will need a 20 amp circuit minimum. Breaker size is rated by the wire size, not the unit you plug into it.
Not necessarily when it comes to welders. NEC Article 630 covers the topic and allows for conductors to be generally undersized for a given breaker size when compared to normal residential wiring.Mike in post #5 hit the nail on the head. The breaker is designed to protect the other elements of the circuit (recepticle, wiring, connectors) and to some extent, the equipment plugged in to it. If the wiring or the recepticle are not sized for 30 amps, but you use a 30 amp breaker, you risk damaging your circuit. If your device plug is not rated for 30 amps, and you use a 30 amp breaker, you risk damaging your device.
The idea is to use the smallest breaker you can (which should be rated lower than everything else in the circuit) that will still handle the load you will draw.
All that said, assuming the plug will physically fit the recepticle, it will work.
Yes. Did you google it? Because ya know what comes up? The HF page and a GJ thread talking about… drum roll, please… the fact that they aren’t really suitable for anything.Did googling for it let you down?
Thanks for pointing that out. Maybe you could provide some specifics that would steer the OP in the right direction given their specific situation if different than has been generally discussed here so far? While some folks are willing/able to read/understand/implement the guidance in the NEC, I feel like that's probably not universal.Not necessarily when it comes to welders. NEC Article 630 covers the topic and allows for conductors to be generally undersized for a given breaker size when compared to normal residential wiring.
Yes. Did you google it? Because ya know what comes up? The HF page and a GJ thread talking about… drum roll, please… the fact that they aren’t really suitable for anything.
I know what a spot welder is. I have a spot welding certification. How’s your reading comprehension?![]()
Spot Welder Applications
For those who think it's easier to annoy you than to Google 'Spot welder applications' themselves.letmegooglethat.com
If you have a spot welding certification, why are you asking a bunch of "wise electricians" what they are good for?I know what a spot welder is. I have a spot welding certification. How’s your reading comprehension?
If you have a spot welding certification, why are you asking a bunch of "wise electricians" what they are good for?
what is that spot welder even good for
that spot welder
that
Without knowing more about the OP's setup there really isn't any way to give more specific advice. We would need to know the wire size and type, length of run (probably not a factor, but just to be safe) and then the outlet/plug setup intended.Thanks for pointing that out. Maybe you could provide some specifics that would steer the OP in the right direction given their specific situation if different than has been generally discussed here so far? While some folks are willing/able to read/understand/implement the guidance in the NEC, I feel like that's probably not universal.
For sure, but Are the lamps pulling 20 amps?If the wire is sized for the load and the device doesn't require the breaker for it's own protection, yes.
How about all those lamps in your house plugged into 20a circuits? Run 20a through that cord and it will get toasty fast
I'm confused on how that's different than your example.For sure, but Are the lamps pulling 20 amps?
If not, wouldn’t that be why the cord is not necessarily heavy?
Something that could pull 20 amps probably has a heavier cord, right?