I am planning to add a 50A RV receptacle and have AL 6-6-6 with 6 ground with OD of 0.717". Will be using Sch 40 conduit for protection from the attic down the wall to the receptacle. It fits loosely in 3/4 PVC conduit but not sure it meets code due to fill. I read someones opinion (not on this site) that since it isn't continuous conduit the 53% fill limit doesn't apply but not sure that's true.
Running the numbers with 3/4" sch 40 PVC it is 76% fill and with 1" it is 47% fill. Do I need 1" conduit or is 3/4 ok?
Running the numbers with 3/4" sch 40 PVC it is 76% fill and with 1" it is 47% fill. Do I need 1" conduit or is 3/4 ok?