I'm installing a new double convection wall oven that requires a bigger breaker/wiring. Manual calls for a 40 amp breaker.
Current set up has the oven wiring (30 amp) and the central air fan (20 amp) running in the same 3/4" FMC that runs 10' into a j box in the attic, is that allowed?
Here is my plan If an oven circuit is allowed to share conduits:
From main panel:
40 amp breaker - 3 6g Thhn wires
20 amp Breaker - 2 12g Thhn wires
1 8g ground wire
All feed into 3/4" FMC to a J box 10' away in attic. (39% conduit fill)
In the attic J box:
the 8g ground will connect to a bar with 3 slots
the 2 12g will wire nut splice to the existing 12/2 NM and run out of the box to the outlet in the attic for the central air fan (NM ground will go to ground bar)
the 3 6g wires will pass through box into 3/4" FMC to the oven Jbox ~40' away
Another 8g ground will go from the ground bar and run along the 3 6g wires to the oven
Current set up has the oven wiring (30 amp) and the central air fan (20 amp) running in the same 3/4" FMC that runs 10' into a j box in the attic, is that allowed?
Here is my plan If an oven circuit is allowed to share conduits:
From main panel:
40 amp breaker - 3 6g Thhn wires
20 amp Breaker - 2 12g Thhn wires
1 8g ground wire
All feed into 3/4" FMC to a J box 10' away in attic. (39% conduit fill)
In the attic J box:
the 8g ground will connect to a bar with 3 slots
the 2 12g will wire nut splice to the existing 12/2 NM and run out of the box to the outlet in the attic for the central air fan (NM ground will go to ground bar)
the 3 6g wires will pass through box into 3/4" FMC to the oven Jbox ~40' away
Another 8g ground will go from the ground bar and run along the 3 6g wires to the oven