Will this smart switch work with a compressor pressure switch?
Pontiac787
New Hampshire
Hi All,
I currently have a standard toggle switch in-line with the pressure switch on my compressor. I would like to be turn the compressor on/off from two different locations. I think the easiest way to accomplish that would be with a smart switch and a remote control. There is no neutral on the pressure switch so would a Lutron Pro switch do the trick? If so, is there anything additional needed? I've seen reference to a bridge or hub when using a no-neutral switch.
This is the switch I'm referring to - Lutron Pro Switch
Thanks!
wyliesdiesels
Modesto, CA
considering you didnt give us any info about your compressor its impossible to answer.
whats the HP rating on your compressor? standard toggle snap switches are not motor rated for more than maybe 1hp.
does your compressor have a starter or does the pressure switch the full load current of the motor?
need more info here
The Cobbler
it doesn't appear to be motor rated , other than 3 amp for a fan, and it has low wattage rating for lighting to . doubtful it will last for a heavier load . maybe if you add a relay to it
LukeOresk
You have a similar problem I had when I was looking at putting my oil furnace in my shop on a smart switch. I was able to get away with this because it’s 3/4 hp rated. With out knowing your hp it’s hard to say how and if it’s possible for you
P
Pontiac787
New Hampshire
The compressor has a mag starter on it and the pressure switch is acting as the relay, no? It’s been a while since I wired it but I think it is only 16 gauge wire (might be 18) going to the switch.
P
Pontiac787
New Hampshire
need more info here
Sorry. I was more interested in the function of this type of switch. 240v 5hp motor with a mag starter.
P
Pontiac787
New Hampshire
I have one of those running the high bay lights in my garage. It does have a higher wattage rating than the Lutron but I think it requires a neutral.
johnre
Portland, OR
The Lutron Pro is a dimmer, and it will not work as a motor starter - it has neither the rating for your compressor, nor is it the correct on/off function.
I solved a similar problem with my 240 V 1.5 HP dust collector system by building a wireless remote with the following key components. It is much more robust than the standard commercial remotes available from woodworking suppliers:
30 A 240 V contactor
Wireless remote
NEMA enclosure
Note that the wireless base unit can operate at either 120 V or 240 V input, and its contacts only drive the A/C starter relay, not the motor directly. It comes with two remotes, so you are covered for your application. I chose a relay that had a 240 V coil on the primary, so it's 240 V throughout the controller and the neutral isn't needed.
Here's what it all looks like finished; I wired it for NEMA 6-20 plug and receptacle - and yes, I do realize I need to wrap red tape around the incoming white 240 V supply cord wire, that's the way it was when I bought it:
dave*99
Coastal NJ
Is there an antenna sticking out of that NEMA box? Hard to tell in the photo.
wyliesdiesels
Modesto, CA
Nope
The mag starter is the relay. The pressure switch is what turns the relay on and off.
Whatever switch you use will need to be rated for 240v.
The lutron is not gonna work.
P
Pontiac787
New Hampshire
Thanks! I didn’t realize the switch was a dimmer. I was going by the photo that just showed the on/off buttons.
fitter30
Peace Valley,mo
Move it to the y wire for the thermostat. Want to kill both the indoor fan second relay if fan switch is on position wire the g wire in series
johnre
Portland, OR
They say right on the [remote device] box ‘Neutral wire Required’
I am aware. That's because it's not switched on the neutral side, only H1, so with 240 V H1 / H2 at the input of the device it would have a switched H1 and an always-hot H2 at the output of the device.
In my case this output only drives the coil in the relay, not the motor, which is fully switched on both H1 and H2 by the relay contacts.
If that's bothersome to anyone, you could instead get a relay with a 120 V coil and bring neutral into the enclosure, so that the circuit for this device and the relay coil are operating on 120 V only.
No, I tested it and it does OK for range even with that pigtail totally contained within the metal enclosure. I need to go only about 30 feet away with my remote, but that's partly through a concrete foundation wall. It advertises a 328 foot range (100 meters), so there's apparently plenty of signal even with the wire not brought out.
P
Pontiac787
New Hampshire
The more I think about it the simplest method may be to just use 2 3-way toggle switches. The switches are will be less than 10’ apart on different levels with no issue running a wire between. I’m only breaking one leg of the wires running to the starter.
johnre
Portland, OR
The issue is that a 3-way switch function is not normally available on a 240 V motor starter switch.
There's a already a lengthy discussion thread on the type of switch needed, here:
P
Pontiac787
New Hampshire
Is a motor rated switch required if it is only switching power to the relay coil?
The compressor in the linked thread wasn’t running a mag starter, just a pressure switch.
dave*99
Coastal NJ
If you post a wiring diagram of your compressor and plan to wire in your switch, other folks will converge on a solution. Without that, GJ is the ultimate speculation machine.
wyliesdiesels
Modesto, CA
no but you dp need a 240v rated 3-way switch. i dont usually see those at the big box stores.
TRWham
East Cobb County, Georgia
No, but it needs to be rated for the voltage, and your control wiring needs to comply with Table 430.72(B)(2) which it may not in your case unless your 16 or 18 gage wire has a separate fuse (7A for 18 and 10A for 16)..