600SL
Well-known member
I'm having a issue understanding the maximum size CB I can put in my Siemens main panel to feed a sub panel. The notes are presented below. The right hand side show's the maximum breaker size is 100A. But the note bellow the table states QPH and HQP type breakers are limited to 100 amps if installed on a circuit capable of delivering fault current > 10,000 amps. Not sure what that means but I would like to know if I can use a 125A breaker with this box to power my sub panel. Not the end of the world if I'm limited to 100amps but a heat pump with E head while welding and compressor coming on could push the limits.