I've got this older saw motor I need to rewrire. I had to take all the wiring off when I got it as it was hard wiped into the deceased owner's basement and lug it up a flight of stairs.

Am I reading this correctly, that for 220V, T1 is hot, T4+T8 are hot, and T2+T3+T5 are wired together in a wire but? The inside of the box has a grounding screw.

How/where could I put a switch on it? I'm assuming I'd need a 20A/250V switch? 20240404_181844.jpg20240404_182154.jpg
 
To avoid these ads, REGISTER NOW!

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
yes that is correct, usually for 240V in the US electrical grids (not too sure about Texas) you used a DPST switch for 240Vac stuff that would break the Hot-Hot connections.... a single pole switch on any legs would work but that would leave one of the legs live.... might be shocking... your choice..
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
got this when it was on sale last week for $8.. now $15 of cause. Probably can find something similar in AMazon.

 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
I've got this older saw motor I need to rewrire. I had to take all the wiring off when I got it as it was hard wiped into the deceased owner's basement and lug it up a flight of stairs.

Am I reading this correctly, that for 220V, T1 is hot, T4+T8 are hot, and T2+T3+T5 are wired together in a wire but? The inside of the box has a grounding screw.

How/where could I put a switch on it? I'm assuming I'd need a 20A/250V switch? 20240404_181844.jpg20240404_182154.jpg
Yes, your understanding of the connections are correct.

The switch needs to be horsepower rated. The 2 mentioned above are horsepower rated BUT the motor has no overload protection in it.

You need to buy a manual starter motor switch that includes overload protection. The overload protection value should be ~ 115% of 9.6Amps.
The manual switch will tell you the correct overload element (Heater) to purchase.

Connect a cord with plug end (6-15P or 6-20P) into manual starter and from it connect to motor.
 

johnre

Well-known member
Joined
Dec 1, 2016
Messages
1,059
Location
Portland, OR
The Leviton MS-302 switches 2 poles.

1712770250203.png

That's a good choice, but it does need an oversize J-Box. Thread about it here:

Received and installed - and thanks to @u2slow , @PCustoms, and others who pointed this issue out and identified a suitable switch series for my 5 HP compressor (well, so-called 5 HP, of course). New switch (left) is massive compared to previous one that was only rated for 1 HP (right):
1709353268106.jpeg

Putting switch in new J-box and wiring it took about half an hour.

But before that could happen, changing out the J-box (the new one is oversized and custom made for this switch, which doesn't fit a standard size) was about six hours - I wanted it mostly recessed so I pulled out the panel, scrolled out the opening, and built a backing brace for it.
1709353588123.jpeg

And the part of this involving removing / reinstalling my compressor panel, which it seems I didn't much design for serviceability and is very hard to get at from behind (compressor sits above it and air reel in back of it), took 4 hours!
1709353649812.jpeg

Now to get on with the basic premise of this thread - I'll have to add back in a pilot light to indicate it's on!
 
OP
M

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
That looks like the one in the post below, just different color?
Yes, your understanding of the connections are correct.

The switch needs to be horsepower rated. The 2 mentioned above are horsepower rated BUT the motor has no overload protection in it.

You need to buy a manual starter motor switch that includes overload protection. The overload protection value should be ~ 115% of 9.6Amps.
The manual switch will tell you the correct overload element (Heater) to purchase.

Connect a cord with plug end (6-15P or 6-20P) into manual starter and from it connect to motor.
Could you please direct me to an "overload element"? I've attached a pic of the cord and plug in going to use...hopefully it's correct.
That's a good choice, but it does need an oversize J-Box. Thread about it here:

Your wiring connections are correct. If it turns the wrong way, swap T5 and T8 and it'll turn the other way.

Also, as noted, the switch will need overload protection. It'll need to be rated at 1.5HP@240 volts and be able to be set to 9.6 amps.
I'm a bit lost on these parts. What is "different" about this motor that it needs so much extra in the wiring department? It didn't have anything like this when I bought it.

Pic of cord and plug. 10/3 cord.

20240409_175337.jpg
 
OP
M

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
I recently bought this at a garage sale not really knowing what to do with it. I'm guessing this would work as a whole unit? Do I need anything else to go with it?

20240410_221535.jpg
20240410_221541.jpg

20240410_221623.jpg

20240410_221647.jpg


20240410_221723.jpg

20240410_221736.jpg

20240410_221806.jpg
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,281
Location
Coastal NJ
That looks like the one in the post below, just different color?
Nope, according to that post, the red one is rated for 1 HP. It is physically smaller etc. I think you have a 1.5HP motor.

1712844281852.png

But as others have said, your motor is not thermally protected. So it was designed to use a motor starter with thermal protection.
Like the one you found at a garage sale. You will need to install the correct size heaters (amperage) for your motor. The N25's that are in there are not rated for the motors amperage.

Oddly enough, the yellow sticky note in your photo says N30 - and that may be correct for your motor. You need 2. Did the motor and starter come from the same yard sale?
 
Last edited:

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,101
Location
Fernley, Nevada, about 30 miles east of Reno.
That starter will work with your motor. As noted, you'll need 2 N30 heaters. They are easy to replace.

Do not do anything to the contacts. If you file or sand them, they won't mate up with each other and they'll fail early. The black stuff you see is silver oxide. It is conductive and won't cause any problems.

If the layer of silver is filed off, the copper below it will arc and cause copper oxide to build up. Copper oxide is not conductive.......

If you absolutely must clean them, a basic pencil eraser works best. It'll clean the oxide off but won't affect the mating surfaces.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
That starter will work with your motor. As noted, you'll need 2 N30 heaters. They are easy to replace.

Do not do anything to the contacts. If you file or sand them, they won't mate up with each other and they'll fail early. The black stuff you see is silver oxide. It is conductive and won't cause any problems.

If the layer of silver is filed off, the copper below it will arc and cause copper oxide to build up. Copper oxide is not conductive.......

If you absolutely must clean them, a basic pencil eraser works best. It'll clean the oxide off but won't affect the mating surfaces.
Thank you for posting the above comment.

If anyone says to file the contacts, that is a sure way to know their advice can be disregarded, manufacturers say not to file the contacts.
 
To avoid these ads, REGISTER NOW!
OP
M

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
Why are you referring to 220?
The nameplate says 230 in 2 places for Pete's sake.
mr-mom-220.gif

So I looked at the saw (it's at my parent's house) and it already has a switch. Made by Rockwell even. If this were going to be constantly used, it might be worthwhile to go to all this extra work. Since it will be used intermittently, is it still necessary? It didn't have one for the 50+ years it's been around. I understand what's "proper" vs "practical".

Here are the pics. It was also $75 which is why I'm not sold on spending $100+ on this thing.

20240411_112412.jpg

20240411_112446.jpg
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
I think you overlooked the motor starter.

I have a Rockwell shaper - mid 90's vintage. It has the same stop/start Pushbutton station. It however is only for control voltage to operate a motor starter. The motor starter has overload protection in it sized for the motor. Your "motor starter" is called a manual starter - i.e. -actuated by hand.

Without overload protection, you risk burning out your motor if it becomes overloaded for any length of time. Cutting heavy lumber, feed rate, pitch, binding, blade sharpness all affect the load placed on the motor.

Think of it like car insurance. Your call.......feeling lucky??
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Those Rockwell devices come in 2 flavors, a maintained motor starting switch, the cover is Rockwell & the starter is made by Furnas Electric, and a control station to be used with Rockwell LVC starters, Low Voltage Control which had a definite purpose contactor, multi tapped 24V control transformer, and either a Furnas, or GE, overload relay, earlier Rockwell tools used Cutler-Hammer art deco starters/control stations, which are quite prized among tool restorers.
 
OP
M

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
Why did this saw not have one originally? Is there a reason the N25 heaters don't work? At a certain point, it will just be cheaper to buy a cheapie saw and throw this one in the scrap heap. I paid $75 for the whole setup, and so far the power cord was $30, plug was $15, manual starter was $20...the saw MIGHT get an hour use per year in the next couple years while I do small projects at my parent's vacation home for them.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,281
Location
Coastal NJ
Why did this saw not have one originally? Is there a reason the N25 heaters don't work? At a certain point, it will just be cheaper to buy a cheapie saw and throw this one in the scrap heap. I paid $75 for the whole setup, and so far the power cord was $30, plug was $15, manual starter was $20...the saw MIGHT get an hour use per year in the next couple years while I do small projects at my parent's vacation home for them.
Heaters are cheap. Look at the chart inside the motor starter. Look at the motor label and see the amps drawn by the motor. Match up the ratings. The N25 heaters will likely shut down your motor well below its capability. Rip a long board and saw trips out when it didn’t need to.
 

kinglake

Well-known member
Joined
Dec 12, 2011
Messages
96
Why did this saw not have one originally? Is there a reason the N25 heaters don't work? At a certain point, it will just be cheaper to buy a cheapie saw and throw this one in the scrap heap. I paid $75 for the whole setup, and so far the power cord was $30, plug was $15, manual starter was $20...the saw MIGHT get an hour use per year in the next couple years while I do small projects at my parent's vacation home for them.
Put the cord and plug on it and use it. At worst, you will burn up the motor. Not likely to happen though.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,281
Location
Coastal NJ

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
Why did this saw not have one originally?
Back when this saw was made motors often cost more than the tools so they were sold separately. This allowed the customer to use a motor that already owned or get a smaller or larger motor for their application.


Is there a reason the N25 heaters don't work?

The N25 heater are for a smaller motor if you use them they will shut down the motor when it pulls more than 6.4 Amps for more than 20 seconds or so. My guess is your motor will pull more than 7 amps before you start cutting anything.

The motor starter protects the motor from being overloaded and being damaged. The last owner decided they did not care if the motor got burned up and was damaged beyond repair. If you feel the same you could replace the heater with some coper wire and use it as a heavy duty switch.

To be safe be sure a green wire from the cord gets connected to the case of the motor starer, the frame of the machine and the motor its self.

Walta
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,281
Location
Coastal NJ
Back when this saw was made motors often cost more than the tools so they were sold separately. This allowed the customer to use a motor that already owned or get a smaller or larger motor for their application.
Yup. My grandfather had a craftsman small table saw / jointer planer combo. One motor ran 2 machines.

There were some machines years ago that had a common hinged mounting plate and you moved your motor from machine to machine as needed.
 